G

gpz900jim

I didnt think these things really existed. I went to see a shower that wasnt working (8.5kw triton shower) I opened the case up and the wire going to the connector was 1.5mm twin and earth. I took the shower off the wall and the 1.5mm cable was twisted together and taped up to the 6mm cable.. No earth was connected. I asked the lady how long the shower had been fitted. She said 18 months. It seems that it had worked ok like that for the last 18 months ?? . No rcd, by the way. I asked who had fitted it. she said "A plumber".
 
8.5 KW through a 1.5 mm cable.... is a little hairy to say the least. The only thing that probably prevented it burning was that it was such a short length. No RCD or earth connection is plain stupidity even for a plumber. Can't you report the idiot?
 
She must have 2 minute showers.

I recently replaced a shower switch that had burned out along with a few cm of the 10mm neutral connected to it (the shower was 9-9.5kw). The owner admitted to spending ages under the shower every day
 
In a former life (I don't do domestic work any longer, as a rule) showers were almost always the one area I would be guaranteed to find issues.

I've seen so many examples of this kind of faeces, it's untrue. 9kW showers run in 0.75 three core flex? No earth? Cable run in copper pipe into the shower enclosure (and not earthed), RCD enclosure fitted in the shower enclosure!!!! Showers "spurred" off the nearest lighting feed.

Without putting too fine a point on it, it was a standard response to show them what a first degree shock burn looks like when modeled by a person, condemn and disconnect the shower (including cutting cable short), and finally pointing out that they wouldn't expect me to plumb the shower, so why expect a plumber to cable it at all, let alone properly.

I ran an "awareness" campaign around my local plumbers many years ago when first in business, offering to do the electrical side of their shower installs, with certification. It got me a lot of work, not only in showers, but also in central heating, and boiler spurs.

It's often a shame these days I think, that there doesn't seem to be any co-operation between trades, and it's something I always suggest to guys kicking off on their own, when I talk to them at trade counters, etc. Find good existing related trades people, and network - help them and help yourself, and build an informal team passing work round among yourselves.

And it's an idea that I think would fly for a lot of guys in this weather/economic climate too.
 
I agree if you stand tall and do a campaign then that will be a sure pull for work.
I've been thinking along those lines but just not ready to stick my neck out that far yet.
 
I have seen this so many times, went to a house some years ago, man had fits after a shower ever day. Checked the shower out found the shower was live in when wet no rcds then.10kw shower 2.5mm T& E no earth. When he had a shower he picked up the shower metal head and wam every day and had a fit. Trading standard / HSE took the plumber who fitted it to court 6 months prison and a big fine and the man had no more fits. Went to a kitchen after a fire this week the insurance had sent people out who had cut all the lighting down took all the socket faces off just pulled the wires apart and when I went in I found all the circuits were still live phone to the HSE/ trading standards are dealing with it, two hours to make safe.The poor home owner had small children could have been so nasty.The kitchen people said they were fine and just to throw the cables (still live ) above what was left of the ceiling to be forgotten.
 
Last edited by a moderator:
I agree if you stand tall and do a campaign then that will be a sure pull for work.
I've been thinking along those lines but just not ready to stick my neck out that far yet.

It's worth doing mate. Gently, mind :)

There's two strands to that though - a campaign to improve trades and public understanding of the correct way to do things, is one.

I think, more essential for now, and we're already seeing evidence in terms of work quantity and so on - is that we need to be finding different ways forward in terms of survival and growth, or at least existence.

For that reason, I think the idea of a loose co-operative with other trades is diamond for now - getting four or five other trades around you who have a vested and mutual interest in recommending you, over any other sparks, and like wise, you for them.

Doing this, there's so many ways in which you can benefit everyone in the network too - opportunities open up that weren't there before, advertising is easier, in all senses, you can promote on the basis that everyone quality checks everyone else on the job, and so on.

I honestly think it's little angles like that which will pull the strongest through this current economic phase - which isn't set to improve drastically for at least a couple of years yet. We're looking at growth of only around 1.5% over the next fiscal year, according to "experts" - which realistically means you won't get any busier on your own than you are now. It's worth noting that some of that "growth" in the economy comes down to things like the increase in VAT, which doesn't benefit us at all, and cuts in services too, which also doesn't really benefit us at all.

Diversity and innovation are your friends at this time, I think. Those who can react to that, and move in new ways will win.

The fundamental problem we are all facing to some extent now too, is that however important safety is, it will ALWAYS be trumped by affordability. Humans will run the risk of death quite happily, so long as they can afford to pay the rent, and eat.

And that translates for us into a major headache in getting rid of cowboys who can "do the job" cheaper than we can by omitting all those "irrelevant" safety features we do, but they don't. Sadly, I think our only way around this, for now, is to think smarter, and try to find ways to provide the proper service, within the budgets available.

What's more worrying, is that the big companies, who got hit hardest in the recession are already using their reserves to discount heavily, to provide at least some of that service, at prices Joe Public will pay. Clearly, us little guys can't afford to do that, and survive, alone.

OK - depressing rant off - it wasn't meant to be doom and gloom, but about being positive and finding a way through the mire Labour and the banks left us with!
 
found one a few months ago wired in 1.5mm flex off the ring main, bathroom done by the plumber , it happens all the time bathroom had been done 18 months ago and was used every day ,, this is why Part P is a complete and utter waste of time !!!!should be renamed Electricians tax
 
Last edited by a moderator:
Good points Bill but this 'co-operative" system as always been around unfortunately with the part P fiasco it as become redundant.

Through out my contracting career I always worked with builders on the co-op system. Extensions, new builds, whatever they ineveitably used the same contractors for plumbing and electrical and the reverse would be the same.

What changed IMO was the part P and the self certification schemes where you now can have plumbers, gas fitters, kitchen fitters getting a Part scope creditation and therefore able to sign off there own minor electrical work.

Just think of the outrage if we were allowed to do our own gas fitting, not that hard to run a bit of copper pipe to a boiler, and then pressure test it, bet it could be taught on a 5 day course and off us sparks go. There would be murders about this, but nothing was done when other trades can be classed competant.

IMO the Part P as done more damage to our industry than all the Eastern European Sparks could ever do. With anyone within the building industry taking a 5 day course to become competant, and now anyone outside the industry can do a 7 week DI course and also be competant.

Said this many many times I'm worried and concerned where my industry is going. It will take several serious incidents to change this state of sorry aafairs, but until then we are an accident waiting to happen.
 
Good points Bill but this 'co-operative" system as always been around unfortunately with the part P fiasco it as become redundant.

Through out my contracting career I always worked with builders on the co-op system. Extensions, new builds, whatever they ineveitably used the same contractors for plumbing and electrical and the reverse would be the same.

What changed IMO was the part P and the self certification schemes where you now can have plumbers, gas fitters, kitchen fitters getting a Part scope creditation and therefore able to sign off there own minor electrical work.

Just think of the outrage if we were allowed to do our own gas fitting, not that hard to run a bit of copper pipe to a boiler, and then pressure test it, bet it could be taught on a 5 day course and off us sparks go. There would be murders about this, but nothing was done when other trades can be classed competant.

IMO the Part P as done more damage to our industry than all the Eastern European Sparks could ever do. With anyone within the building industry taking a 5 day course to become competant, and now anyone outside the industry can do a 7 week DI course and also be competant.

Said this many many times I'm worried and concerned where my industry is going. It will take several serious incidents to change this state of sorry aafairs, but until then we are an accident waiting to happen.

I think this is true, Malcolm, sadly. Part P as currently implemented is a disaster, and I don't think there's many here who would disagree. It was a major factor in our (my) moving away from domestic work altogether.

The argument about running gas was one which was pushed around a lot at the time Part P was first mooted too - and again, Corgi, at the time, made so much noise about how dangerous it would be for other trades to start running in gas lines, etc.

We are in the same boat now with Part P, you're right.

But, maybe a little idealistically, I still think we can make some sort of advantage out of it with the right education/advertising - encouraging some of these other trades to give up their Part P and keep the fees is one way - and really, financial benefit is probably the major way in which any co-op will successfully bond at this point.

The motivation behind Part P, and the 5 week wonder courses, was intended to improve safety, in terms of competence. As you point out, that has been abused to the extreme, and is also not policed at all. The reality is, as you say, that we have "ex-street sweepers" now claiming to be qualified electricians, who can notify their own work, and that seems to satisfy everyone until the place burns down - or more usually until one of us notices, shows the work up to be the crap it is, and then get lambasted because we're just out to make a quid.

I understand your points totally mate - and agree - but in part it was exactly that which we need to find ways around too, for everyone's benefits. I don't know that it'll be easy - it won't, but part of it needs to be about overcoming every objection, and making it work, for sure.
 
Where will it all end, Part P was brought out with the best intentions to stop have a go Harry. As we were already working to BS7671 and HSE,EAWA we were all doing it how it should be done and didn`t need anymore red tape. What was wrong with the good old days of the MEB coming round and signing it off and doing the meter work. After so many years of it working why did they throw it all up in the air 5 years down the road and Part P doesn`t work and the customer always wants the cheapest job, so your eastern european spark on £35 a day or 5 day wonder will always be cheaper as we can not compete with all the overheads of me.
 
Understanding all above but also many outfits, one man bands etc were doing electrical work unqualified before Part P and then when Part P courses come along at an affordable duration these same outfits done the course and put it on there van. They must do a safer job after some training than none. That has to be an improvement although not ideal.

As far as competence is concerned that is up to the individual and the scheme provider not the 1,3,5 day, or 3,4 yr course.

IMO if your running from the Part P / domestic situation then your fueling what you are disagreeing with when you should be standing strong and enduring / ensuring correction under the label of safety.

Campaign as was mentioned earlier.

Why oh why has Part P not been given proper pubic awareness alike Gas Safe?
I'm sure this will happen quickly if as many Part P prosecutions take place as the gas fitters?

I'm sure the above will agree but we have to keep our nose on the bread trail.
 
Last edited by a moderator:
I agree with your post and found it insightful, all except this;
The fundamental problem we are all facing to some extent now too, is that however important safety is, it will ALWAYS be trumped by affordability. Humans will run the risk of death quite happily, so long as they can afford to pay the rent, and eat.

And that translates for us into a major headache in getting rid of cowboys who can "do the job" cheaper than we can by omitting all those "irrelevant" safety features we do, but they don't.

I think as tradesmen it isn't your responsibility to combat illegal cowboys who endanger lives, also as a customer price shouldn't be able to trump safety, surely that's what legislation is for? Enforcing legislation is the responsibility is the job of the authorities.
 
Understanding all above but also many outfits, one man bands etc were doing electrical work unqualified before Part P and then when Part P courses come along at an affordable duration these same outfits done the course and put it on there van. They must do a safer job after some training than none.

Certainly, they should have a better understanding of requirements after the (Part P specific) training than before. It doesn't follow that they will then do the job any better though.

I know many firms who have openly admitted to getting some of their staff through a Part P course, simply to be able to wear the badge, and carry on doing what they already were - e.g. boiler fits, kitchen and bathroom work.

As far as competence is concerned that is up to the individual and the scheme provider not the 1,3,5 day, or 3,4 yr course.

Competence is always up to the individual. The courses *should* help the competence, but only if the individual is willing to take on the education provided and then apply it consistently. As for the scheme providers, they should be assessing the competence of the individual against consistent criteria every time, and should NOT be doing anything else at all, beyond stating that an individual is, or is not meeting the requirements for the scheme, and by extension (if the scheme is correctly designed), the requirements for a safe and practical installation.

IMO if your running from the Part P then your fueling what you are disagreeing with when you should be standing strong and enuring correction under the label of safety.

In an ideal world, perhaps. The reality, however, is that legislation has forced many very competent, and very qualified individuals into a system which does not benefit them in any way at all - in fact, which takes away from the very reasons most of them bothered to do the training, become competent, and to uphold the rules in the first place.

The real effect of Part P on the whole, has been to allow an influx of cowboys which otherwise would not have had any advantage, to gain footholds in ways never before possible. Ten years ago, it would have been inconceivable that a kitchen fitter, or DIY warehouse, for example, would undertake anything like the scale or scope of electrical work they do now. Part P and its insistence on scheme registration has simply allowed them to gain footholds in areas where they wouldn't have before.

Simply, Part P schemes say to most applicants - "Pay the money and carry on". It isn't like Part P work is any more policed than any other aspect of a tradesman's work in any other field, or any more than a typical electrician's work was prior to Part P.

I say again, that the only time prosecutions are ever going to be likely is where there is an incident and investigation is unavoidable - but mostly, it is an exercise in paperwork, and money generation, other than that.

Without the policing, and proper inspection of work completed under the schemes available (which doesn't happen), nothing at all will change. The only real benefit is that people are aware enough of Part P requirements, that it would look suspicious for any domestic electrician to claim they were carrying out domestic work without such scheme membership - and that would probably attract scrutiny in itself.

Hence, the industry as far as domestic work is concerned, is over a barrel by means of regulations which do not do what they set out to do at all, in any way, at all.

We all know that Part P has failed, utterly, to make any improvements to safety whatever, because it cannot police what actually happens every day.

Campaign as was mentioned earlier.

National campaigns might help, but for the moment, given the state of things, it will be very much down to us, electricians working every day and having to face the very many issues ill-considered legislation produce, to make our customers aware of what they really need to know to make informed, safe, decisions, within the framework dumped on us.

Why oh why has Part P not been given proper pubic awareness alike Gas Safe?

Primarily because gas safety is a legal Act in its own right, and Part P is only one part of a hotch potch of building regulations, designed to do too many things in a limited set of legislation.

Electricity has never been treated as a dangerous product in the way gas has, and in part, that is a testimony to the track record of electrical manufacturers to make their products as safe as possible despite legislative attempts to insinuate otherwise.

It is also a testimony to the majority of electricians out there in the UK who do work to exceptionally high standards consistently.

I'm sure this will happen quickly if as many Part P prosecutions take place as the gas fitters?

As said, prosecutions will only start to take any sort of hold if the policing is there in the first place. Gas Safe was set up as a funded partnership specifically to police Gas work, and receives an amount of funding on top of registration fees to ensure it does police as far as it can (which is still only around one in every two hundred notifiable gas works).

However, another reason you won't see prosecutions quite simply is that it is not cost effective to prosecute minor fails and only the very worst of identified no-compliances will ever be prosecuted - those resulting in really dangerous safety issues, or fire - or obviously, death.

What Part P has given us, is only proof that whether "policing" is voluntary, such as NICEIC or ECA, or legislation driven such as NAPIT and ELECSA schemes for Part P, they all fail on common ground - real policing. Until there is some way of rigorously enforcing regulations, or those who claim to work to them, it doesn't matter at all how much we legislate, or create voluntary schemes, there will always be those working around them, without care or qualification. They will simply continue to play the odds.

I'm sure the above will agree but we have to keep our nose on the bread trail.

Well, this is true, but I think for any effective changes it is necessary that this time around (the pending review in 2013) that the voices of real electricians actually working at the coal face every day are actually heard this time, and the advice we have to offer heeded, for once.

Only by working to the very highest standards we can, and continuing to educate public as we each try to, will awareness of the need for care and safety in electricity ever get heard.

One of the most effective ways, I guess, for doing that would be a national hall of shame - if not for individuals carrying out dangerous work, at least for photos of the results of dangerous work.
 
I agree with your post and found it insightful, all except this;


I think as tradesmen it isn't your responsibility to combat illegal cowboys who endanger lives, also as a customer price shouldn't be able to trump safety, surely that's what legislation is for? Enforcing legislation is the responsibility is the job of the authorities.

Hey Marvo

I agree with you totally - but that would be the ideal world we all want.

If, as tradesmen, we don't shout about those taking shortcuts, completing dangerous work, and so forth, who will?

Yes, legislation is there, or should be, to combat these types, but, as I say, without policing it just won't ever happen - unqualified or inexperienced folks will get away with sub-standard and dangerous work, because there's nobody there to point it out, or rectify it until disaster strikes - a fire, or a death, or often at best, a serious injury.

Where such work results in faults only, the sad truth is that often the tradesman coming in and rectifying it simply fixes the fault, bitches about the bad previous work, and moves on. A lot of decent guys have limited means, time, or knowledge to push complaints through the legislated channels - and if and when they do, they get met with total inertia, a lack of interest, and brick wall after brick wall. Sometimes, they end up bearing the brunt of the investigation, if there ever is one too.

And if trades people - those with the skill, knowledge, and understanding to know a job is wrong - say nothing, how is the end customer ever going to know they're stuck with dangerous work, until it is too late?

I believe that was exactly my argument - that the legislation *should* protect the consumer/customer. It never will until such is properly policed in some way, and the means we have for policing the work carried out is currently woefully inadequate, and likely to remain that way.

As for cost versus safety - well, that's just human nature. It's something we're never, ever going to beat until public attitude changes significantly - the temptation for a bargain is just too great.

Most customers won't look past price, because there is a general assumption that if you SAY you can install electrical items, you are believed - and if one guys saying it says £1000 properly done, and the next says £250 no questions, who're you going to choose?

It sadly remains a fundamental truth that customers, and especially domestic customers, will choose on the basis of cost over safety every time - to the majority a piece of paper claiming the work to be safe is just not that essential if they can see the ten extra sockets, or new light or whatever they wanted.

A big part of my point, particularly relating to Part P, is that it is ill-considered legislation, which may work on paper and on the basis of "should" - but doesn't work at all in practice. All it has really achieved is to penalise the very group it was initially intended to protect - both electricians and customers. And it will remain that way all the time it cannot be policed properly.

Sad, but I guess that's the difference between reality, and what should be.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
unbelievable
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
19
Unsolved
--

Advert

Thread statistics

Created
gpz900jim,
Last reply from
ian.settle1,
Replies
19
Views
2,778

Advert

Back
Top