The underfloor heating controller says it will be able to pull a maximum of 16 Amps.

The supply is from a 20 RCBO. 2.5mm Twin and earth to a 13 Amp switched fused spur. The load side of the spur feeds the underfloor heating controller.

The owner is saying that if for what ever reason the underfloor heating controller was pulling 18 Amps, the fuse spur will not blow. I know this is the case as 13 Amp fuse will take around 19 Amps for a long period of time. The undefloor heating has been designed to take 8 Amps but from an electrical point of view is this circuit unsafe in anyway?

Help would be appreciated
 
1. what's the kw rating of the mat?

2. how has the customer arrived at this figure of 18A?

3. have you done any testing?

answer the above and you may get some help.
 
The underfloor heating controller says it will be able to pull a maximum of 16 Amps.

The supply is from a 20 RCBO. 2.5mm Twin and earth to a 13 Amp switched fused spur. The load side of the spur feeds the underfloor heating controller.

The owner is saying that if for what ever reason the underfloor heating controller was pulling 18 Amps, the fuse spur will not blow. I know this is the case as 13 Amp fuse will take around 19 Amps for a long period of time. The undefloor heating has been designed to take 8 Amps but from an electrical point of view is this circuit unsafe in anyway?

Help would be appreciated

The controller does not pull 16 amps , it has a maximum rating of 16 amps .

You say the total load of the mat is 8 amps so what is the problem ?
 

Reply to Underfloor heating Controller in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
Conversation developed with a middle aged lady who has recently lost her husband. Note to self, stop walking dog around the graveyard Anyway...
Replies
5
Views
1K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock