Cool thanks for the help. It's a split load rcd board. I'm going there Friday so will let you know how it goes.
I am not sure which reg in BGB, but I think you are not allowed to work on bank holidays.
I hope so.
PICK was talking to the wholesaler and they said about a room only stat!!?? One that doesn't use the sensor in the floor. What's your views on these?
If it is the sensor how would you fix this problem?
Would you have to rip the floor up?
I am asking because the lady up the road thinks her underfloor heating is not switching off properly and the room is overly warm.
Have you measured the resistance? I think its for every degree celcius it is below 25 you add 400ohms to the value, so say its a 10k probe at 25 degrees then at 20 degrees it would be 12k, it could be a 12k or 15k probe but the same principle applies, thats what i've always gone on anywayBut the sensor/floor is stone cold. So getting to 25 degrees is impossible. This is an old installation so I'm not sure where the sensor is located. (In the floor)
I've never done underfloor heating so this it's a learning curve for me.
What else could it be?
The sensor also has to match the thermostat too otherwise it will send it the wrong information so you need to measure the probe resistance and check what the thermostat needsIf it is the sensor how would you fix this problem?
Would you have to rip the floor up?
I am asking because the lady up the road thinks her underfloor heating is not switching off properly and the room is overly warm.