And an almost superstitious
you can sing this when you thinking about it Vort.;)

upload_2019-5-1_20-22-2.png
 
  • Funny
Reactions: 1 person
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.

Loving Extraneousness!! That should definitely be a word lol
 
  • Like
Reactions: Baddegg and DPG
Some good posts!

I agree, it can be almost impossible to eliminate all parallel paths so an extraneousness test (pinched from @wirepuller :)) isn't going to be that reliable.

I think I'll have a chat with my assessor when he comes and see what he says. Until then, I'll flip a coin to see if I'm going to bond! o_O
 
I don't think it is so hard to determine.

Parallel paths via cpc's will be a low impedance back to MET. You therefore won't know if it was extraneous as you now can't sensibly prove it anymore without disconnecting too much stuff.

If pipework it is at earth potential via a cpc even though it was not extraneous in its own right, you won't do any harm by bonding it, you are just safeguarding if it is truly extraneous.

Most of the sparks at firm I work for don't understand the difference between earthing and bonding lol........let alone making a decision if they should to install it haha
 
I don’t think I’d like to be the one taking that photo - he seems a little miffed!
he has every right to be miffed, as Sitting Bull and the S0iux took all the credit for wiping out Custard and his blue bellies at Little Big Horn
 
  • Agree
Reactions: Rpa07
Why are you all still going on about this subject? There is nothing to question as all the answers are already in this book.
 
As an Amazon Associate we earn from qualifying purchases.
I thought aslong as it exceeded 7.67k ohms it is not to be considered an extraneous conductive part.
 
Surely if there is an insulated incoming service pipe or even a 3 inch insulating piece between metal incoming and installation pipework then it's impossible for a potential to be introduced from outside the building ? And therefore bonding is not required in such circumstances ?
 
You can't earth plastic end of story. don't be a dick.
Do you earth isolated sections of any sort of pipe.... water/oil etc etc??
My answer is probably not, it's your call.
BUT BUT
I have 2 tests to ask
1 IS IT EXPOSED METAL( OF ANY KIND) THAT HAS THE POTENTIAL TO BECOME ALIVE??????
If yes then the answer must be to earth bond it
2 What would be your defense in the coroners court?

Remember the regs are designed to confuse sparkies by legal numpties.
 
I thought aslong as it exceeded 7.67k ohms it is not to be considered an extraneous conductive part.
no. the figure is 22K Ohms. 7.67K is the value of a L-E earth fault or leakage that would trip a 30mA RCD.
 
You can't earth plastic end of story. don't be a dick.
Do you earth isolated sections of any sort of pipe.... water/oil etc etc??
My answer is probably not, it's your call.
BUT BUT
I have 2 tests to ask
1 IS IT EXPOSED METAL( OF ANY KIND) THAT HAS THE POTENTIAL TO BECOME ALIVE??????
If yes then the answer must be to earth bond it
2 What would be your defense in the coroners court?

Remember the regs are designed to confuse sparkies by legal numpties.
Exposed metal that is likely to become live under fault conditions will be or should be earthed, that is a requirement for an exposed conductive part. That is nothing whatsoever to do with bonding.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Understanding the new regulation regarding Main Bonding.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Deleted member 9648,
Replies
32
Views
5,517

Advert