Regulation 411.3.1.2 states ....

Main bonding conductors shall connect to the main earthing terminal extraneous conductive parts.

It then goes on to say...

'Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding'.

Lets say we have a water pipe coming into the house in the plastic blue pipe, from then on its metal. The above reg makes me believe this does not need Main bonding, is that correct?

The above reg does not suggest we test the water pipe to see if it extraneous. It just says we have to bond extraneous parts, then it says not to bond if they come in to the house in an insulating section.

If we do test the water pipe it is likely that it will test at 1 or 2 ohms to earth (probably as it is usually connected to earth somewhere within the premises). Does this reg still imply not to bond in this case when we can clearly see an insulating section at point of entry?
 
Scolmore Electrical Products
This official sponsor may provide discounts for members

GBDamo

-
Supporter
That's how I read it.

plastic coming in, all plastic pipe work = no bond
plastic coming in, all metallic pipe work = no bond
metal coming in, immediately to plastic or a section of = no bond
metal coming in, immediately metallic pipework = bond

This doesn't however mean that pipework that enters in plastic doesn't at some point revert to metal and then creates an extraneous path which may or may not need bonding.

hope that clears it up for you.
 

Charlie_

-
Arms
Same with oil pipes, there’re usually insulated and then we bond at a concealed section.
Incoming Gas pipes are usually insulated
How will a section of insulation stop it from being extraneous??
 
Same with oil pipes, there’re usually insulated and then we bond at a concealed section.
Incoming Gas pipes are usually insulated
How will a section of insulation stop it from being extraneous??
Exactly,who makes these regs,plastic makes it not extraneous.
 

ChrisElectrical88

-
Mentor
Arms
Esteemed
As you have mentioned already, measure resistance to MET from metallic pipework. <22Kohms = bond.
Exactly this, belts and braces this way and your not just seeing a section of plastic and saying no bond. Obviously make sure parellel patha are disconnected first.

Made a post about a month ago on this when i was undecided. Metal coming in streight onto a plastic section then back to metal after the stoptap to the rest of the house. Didnt bond it as the IR reading from the MET to consumer side of the stoptap was around 30k.
 

buzzlightyear

-
Arms
Esteemed
That's how I read it.

plastic coming in, all plastic pipe work = no bond
plastic coming in, all metallic pipe work = no bond
metal coming in, immediately to plastic or a section of = no bond
metal coming in, immediately metallic pipework = bond

This doesn't however mean that pipework that enters in plastic doesn't at some point revert to metal and then creates an extraneous path which may or may not need bonding.

hope that clears it up for you.
I'm glad some one cleared that up thanks Geronimo :)
 

Pete999

-
Arms
Esteemed
No mate he had an Apache on his head, and ut wasn't his own hair never had Head and Shoulders in those days.
 
D

Deleted member 9648

As you have mentioned already, measure resistance to MET from metallic pipework. <22Kohms = bond.
Obviously make sure parellel patha are disconnected first.
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.
 

GBDamo

-
Supporter
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.
Especially in a 32nd floor flat!!
 

ChrisElectrical88

-
Mentor
Arms
Esteemed
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.
I had the on site plumber take a small section out right after the stop tap so i could test it which eliminated all parellel paths lol. Serched everywhere are there was no other extraneous parts. I thibk the reason i got 30KOhms was resistance through the wat or i would have had greater than 99MOhms
 
T

The Ghost

Ever since I started electrics back in 1961 bonding/equipotential cross bonding extraneous metal has been it seems a dark art. With a myriad of opinions on it most wrong. And an almost superstitious "...if it's metal bond it!.." approach. I think in this case it is simpler than we may overthink it is. One caution though, I have been in houses that start with plastic to copper. The copper wends its way through the property to the back bath and or kitchen but goes sub floor in cement so in such a case...??? It is only that there is not one rule fits all a careful survey needs to be done to be sure bonding is not needed as @wirepuller said "...a careful visual inspection..." is required.
 

TJ Anderson

-
Mentor
Arms
Esteemed
It's almost impossible to eliminate parallel paths, if there's a combi for example the gas service will be mechanically joined to the water pipes. The test for extraneousness (I just made that word up) is generally unreliable and I prefer to combine it with a visual assessment of how likely a water pipe is to become extraneous when entirely within a building. Unless the building is steel framed the likelihood is minimal.
Loving Extraneousness!! That should definitely be a word lol
 

happyhippydad

-
Arms
Esteemed
  • Thread Starter Thread Starter
  • #23
Some good posts!

I agree, it can be almost impossible to eliminate all parallel paths so an extraneousness test (pinched from @wirepuller :)) isn't going to be that reliable.

I think I'll have a chat with my assessor when he comes and see what he says. Until then, I'll flip a coin to see if I'm going to bond! o_O
 

TJ Anderson

-
Mentor
Arms
Esteemed
I don't think it is so hard to determine.

Parallel paths via cpc's will be a low impedance back to MET. You therefore won't know if it was extraneous as you now can't sensibly prove it anymore without disconnecting too much stuff.

If pipework it is at earth potential via a cpc even though it was not extraneous in its own right, you won't do any harm by bonding it, you are just safeguarding if it is truly extraneous.

Most of the sparks at firm I work for don't understand the difference between earthing and bonding lol........let alone making a decision if they should to install it haha
 

telectrix

-
Mentor
Arms
Esteemed
I don’t think I’d like to be the one taking that photo - he seems a little miffed!
he has every right to be miffed, as Sitting Bull and the S0iux took all the credit for wiping out Custard and his blue bellies at Little Big Horn
 

Dave OCD

-
Mentor
Arms
Esteemed
Surely if there is an insulated incoming service pipe or even a 3 inch insulating piece between metal incoming and installation pipework then it's impossible for a potential to be introduced from outside the building ? And therefore bonding is not required in such circumstances ?
 
You can't earth plastic end of story. don't be a dick.
Do you earth isolated sections of any sort of pipe.... water/oil etc etc??
My answer is probably not, it's your call.
BUT BUT
I have 2 tests to ask
1 IS IT EXPOSED METAL( OF ANY KIND) THAT HAS THE POTENTIAL TO BECOME ALIVE??????
If yes then the answer must be to earth bond it
2 What would be your defense in the coroners court?

Remember the regs are designed to confuse sparkies by legal numpties.
 
D

Deleted member 9648

You can't earth plastic end of story. don't be a dick.
Do you earth isolated sections of any sort of pipe.... water/oil etc etc??
My answer is probably not, it's your call.
BUT BUT
I have 2 tests to ask
1 IS IT EXPOSED METAL( OF ANY KIND) THAT HAS THE POTENTIAL TO BECOME ALIVE??????
If yes then the answer must be to earth bond it
2 What would be your defense in the coroners court?

Remember the regs are designed to confuse sparkies by legal numpties.
Exposed metal that is likely to become live under fault conditions will be or should be earthed, that is a requirement for an exposed conductive part. That is nothing whatsoever to do with bonding.
 