Called out to a semi-detatched rental property today...TT, semi-enclosed wired fuse board, 4-way with a 500mA Earth Leakage Voltage main switch (60a). The customer has removed the 5a lighting fuse because the EL switch trips after between 30 seconds and 15-20 minutes. There's a suspicion that when this trips it also takes out next door too (not in so can't check what they have).
Western Power have been out and checked the supply side (so I'm informed). Not sure what they've checked.
- Visually checked, no obvious faults on the lighting circuit
- Checked the usual ceiling roses, etc
- Bonding is good
- Ze is 18.4 Ohms (pretty good eh?)
- A couple of the rooms have mains voltage halogens/LEDs and dining room has a set of LV downlights
- Adding the fuse and switching all circuits on/off does not produce a trip
- Property's earth rod is under an extension floor but measures well. It's probably about 7-8m away from next door's rod (which looks fairly new)
I've suggested we change the EL switch to a proper main switch and 30mA RCD anyway. Would be a completely new 6 way board but budget is restricted. When I go back I'll do the usual IR but I figure this isn't a simple fault...what could cause a delayed action trip?
Ideas appreciated!
Called out to a semi-detatched rental property today...TT, semi-enclosed wired fuse board, 4-way with a 500mA Earth Leakage Voltage main switch (60a). The customer has removed the 5a lighting fuse because the EL switch trips after between 30 seconds and 15-20 minutes. There's a suspicion that when this trips it also takes out next door too (not in so can't check what they have).
Western Power have been out and checked the supply side (so I'm informed). Not sure what they've checked.
- Visually checked, no obvious faults on the lighting circuit
- Checked the usual ceiling roses, etc
- Bonding is good
- Ze is 18.4 Ohms (pretty good eh?)
- A couple of the rooms have mains voltage halogens/LEDs and dining room has a set of LV downlights
- Adding the fuse and switching all circuits on/off does not produce a trip
- Property's earth rod is under an extension floor but measures well. It's probably about 7-8m away from next door's rod (which looks fairly new)
I've suggested we change the EL switch to a proper main switch and 30mA RCD anyway. Would be a completely new 6 way board but budget is restricted. When I go back I'll do the usual IR but I figure this isn't a simple fault...what could cause a delayed action trip?
Ideas appreciated!