If the CCC reduction is less than 2 meters no code....
Assuming you're invoking the 3m rule to allow a cable which fails the adiabatic on the fault current, that only applie where both fault protection is omitted (vaporising the cpc probably counts as omission) And, if the cable is unlikely to suffer damage.
T&e in a wall wouldn't comply with the latter, but if it's rcd protected then that could cover the fault protection.
Not sure how the ocpd over 32a would be covered for supplying an accessory though.
I'm not an electrician though!
 
There is no danger to not marking CPCs as green and yellow but that would still be a C3.
Why would it be.
It’s a non compliance which does not give rise to any danger if your talking about the cpc marked green only.
No sleeving then yeah C3 because there is a safety aspect which needs addressing as you are increasing the likelihood of the cpc coming into contact with live parts.
 
Why would it be.
It’s a non compliance which does not give rise to any danger if your talking about the cpc marked green only.
No sleeving then yeah C3 because there is a safety aspect which needs addressing as you are increasing the likelihood of the cpc coming into contact with live parts.

Which is the exact point of a C3. Something that does not give rise to danger but could be improved to meet BS7671.
 
Anybody got any thoughts on my question in #6? What is the maximum permissible MCB rating feeding a 13A BS1363 socket outlet? I would expect the CPC to be OK adiabatically for a B40, but what is the short-circuit rating of the socket and what backup protection is required for things plugged into it? Especially things like wall warts that don't contain a BS1362 HRC fuse.
 
I did investigate this by Googling but found no answer. You can get busbar systems with unfused tap offs in offices with 40 or 50A protective devices.
 
Which is the exact point of a C3. Something that does not give rise to danger but could be improved to meet BS7671.
BS7671 requires us to comment on and apply a code to items which are either dangerous or may give rise to danger.
 
Which is the exact point of a C3. Something that does not give rise to danger but could be improved to meet BS7671.

C3 should be for recommendations for improvement for safety, not purely for the sake of complying with bs7671.

If it was purely recommendations that could improve compliance with BS7671 then all pre-harmonisation cable would automatically be a C3 just for being the wrong colour.
 