I think at times it is difficult to Code something which is a lash up.
Assuming you're invoking the 3m rule to allow a cable which fails the adiabatic on the fault current, that only applie where both fault protection is omitted (vaporising the cpc probably counts as omission) And, if the cable is unlikely to suffer damage.If the CCC reduction is less than 2 meters no code....
If there’s no danger why does it warrant any code?
I think at times it is difficult to Code something which is a lash up.
Why would it be.There is no danger to not marking CPCs as green and yellow but that would still be a C3.
Why would it be.
It’s a non compliance which does not give rise to any danger if your talking about the cpc marked green only.
No sleeving then yeah C3 because there is a safety aspect which needs addressing as you are increasing the likelihood of the cpc coming into contact with live parts.
Anyone want to enlighten me as to what
"air BnB"is?
Pete999 queried it in previous post and no reply as yet.
BS7671 requires us to comment on and apply a code to items which are either dangerous or may give rise to danger.Which is the exact point of a C3. Something that does not give rise to danger but could be improved to meet BS7671.
Which is the exact point of a C3. Something that does not give rise to danger but could be improved to meet BS7671.