Hi All, better news... the 1st electrician charged £75 for checking the wiring of the 2 MCBs and then wanted a few days to find the problem and more £££. I told another electrician who said No charge if I don't find anything within 1 hour..lol I thought. Anyway he wanted to just have a look at all the sockets in the house at first, he then switched off the MCBs in question and went back to a blanked off socket in the kitchen with tester in hand and bugger me he found a block with 2 cables connected, disconnected them and found that MCB1 is upstairs/downstairs and MCB2
is kitchen and down stairs bathroom. He made both cables safe and said he as seen it loads of times and only charged me £45 but did say that all could do with updated consumer unit and wiring. At least the 2 circuits are now separated and should be safer. I suppose most of you have seen this too?
[automerge]1569253826[/automerge]
davesparks...I forgot to mention that nothing was done by the first electrician to make things safe, he just left..
is kitchen and down stairs bathroom. He made both cables safe and said he as seen it loads of times and only charged me £45 but did say that all could do with updated consumer unit and wiring. At least the 2 circuits are now separated and should be safer. I suppose most of you have seen this too?
[automerge]1569253826[/automerge]
davesparks...I forgot to mention that nothing was done by the first electrician to make things safe, he just left..