i would have had no problem using that flex , brown sleeving on both ends whats the problem , common sense over rules the the regs sometimes , tin hat firmly on
Problem is when, as mentioned, someone taps into a cable, sees green & yeller, assumes its a cpc.....etc
as long as the fan was classII and there was no alternative, i might be tempted.
Yes Class II, tempting isn't it. i didn't though as I felt it was just wrong. The problem was the flex was buried in the wall and I really wanted to swap it for a bit of three core, but though hmmm I could use that CPC as its not being used... It was a conductor like the others, so its not like it didnt have any insulation or a smaller CSA.
It doesn't. If it's over sleeved at the end than its ok.
Unless it's a single core cable which can not be sleeved over.
But as darkwood says it's not good practice...
Thats not the way I read the reg, it says green and yellow cables throughout their length shall only be used as a protective conductor, the oversleeve bit is when you mark the ends with a blue indication for PEN conductors.
That's where I was going with it, I know If I cut into a cable and i saw a green / yellow, I probably wouldn't give it any thought and think, yep that's the earth. I think its a good idea to use a CPC as a CPC only and nothing else.
I think if you start using whats really seen to be an earth throughout its length as a live conductor, you are kind of cutting corners in a way and your standards (if you have any) will probably start going down hill, personally I would rather do the right thing and tell the customer, that's going to cost you, you need a new bit of cable.
The two regs in question are here, in case anyone hasn't got the regs with them:
514.4.2 Protective conductor
The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor
and this combination shall not be used for any other purpose. In this combination one of the colours shall cover at
least 30 % and at most 70 % of the surface being coloured, while the other colour shall cover the remainder of the
surface.
Single-core cables that are coloured green-and-yellow throughout their length shall only be used as a protective
conductor and shall not be overmarked at their terminations, except as permitted by Regulation 514.4.3.
A bare conductor or busbar used as a protective conductor shall be identified, where necessary, by equal green-andyellow
stripes, each not less than 15 mm and not more than 100 mm wide, close together, either throughout the
length of the conductor or in each compartment and unit and at each accessible position.
514.4.3 PEN conductor
A PEN conductor shall, when insulated, be marked by one of the following methods:
(i) Green-and-yellow throughout its length with, in addition, blue markings at the terminations
(ii) Blue throughout its length with, in addition, green-and-yellow markings at the terminations.
Has it already been said?
Whether or not oversleeving the cpc is allowed, it cannot normally be done while complying with 412.2.3.2
Single-core cables that are coloured green-and-yellow throughout their length shall only be used as a protective conductor and shall not be overmarked at their terminations
I think that really makes it quite clear.
I think its rather laughable that the NICEIC have actually condoned it in an article.
Yes they are trying to re write the regs. Lets look at this from another aspect, where in the regs does it say it is acceptable to use a green and yellow conductor for a live conductor even if the conductor is marked? It won't, it just won't.