and then run an earth separate?
Single or multicore cable, is it buried, in trunking or conduit, or clipped directWe’ve pulled in a 185 cable just and realised that we need a neutral. It has 4 cores, brown, black, grey and earth. Can we use the earth as a neutral if we shrink wrap it with neutral sleeve and then run an earth separate? It’s a tri-rated cable, so no armoured to use as earth.
Single or multicore cable, is it buried, in trunking or conduit, or clipped direct
Could be on ladder rack, or tray.
Yes you can over sleeve the earth core as neutral and pull in a separate earth.
The separate earth can then enter any ferrous magnetic enclosures separately from the 4 core, although doing such is only normally allowed for SWA cables.
You can have multi core tri-rated cables.
You’ll have to excuse me if I use the incorrect terminology. I’m basically an apprentice and have been set this as a task to find out. So it’s 4 core flexi I think they call it. Big thick black cable with no amouring, just 4 cores It’s runs under the floor and then up and onto ladder
It's obviously a H07RN multicore.Well I don’t know. I’ve pulled in a multi core this week and it was called tri-rated by all the sparks. I will picture it tomorrow
Don’t understand why there’s any debate?Now that we know its not actually tri rated cable yes, ladder or tray seems more likely.
There's an interesting debate to be had on whether it is ever allowed, for SWA or anything else.
It's called tri-flexNever heard of tri-rated flexible cable. There are rubber cables available in that size and if it is a long run someone has made a serious error.
It's called tri-flex
It's also mechanically strong.
I one time drove a genie MEWP over a live 50mm 5 core flex.
If the cable is installed in some kind of metallic containment then use the containment as the cpc, size permitting of course.We’ve pulled in a 185 cable just and realised that we need a neutral. It has 4 cores, brown, black, grey and earth. Can we use the earth as a neutral if we shrink wrap it with neutral sleeve and then run an earth separate? It’s a tri-rated cable, so no armoured to use as earth.
Don’t understand why there’s any debate?
521.5.1 Ferromagnetic enclosures: electromagnetic effects
The conductors of an AC circuit installed in a ferromagnetic enclosure shall be arranged so that all line conductors and the neutral conductor, if any, and the appropriate protective conductor are contained within the same enclosure.
Where such conductors enter a ferrous enclosure, they shall be arranged such that the conductors are only collectively surrounded by ferromagnetic material.
These requirements do not preclude the use of an additional protective conductor in parallel with the steel wire armouring of a cable where such is required to comply with the requirements of the appropriate regulations in Chapters 41 and 54. It is permitted for such an additional protective conductor to enter the ferrous enclosure individually.
Didn't take a fidge out of it.I bet it looked like a snake,run over,on a cattle grid....![]()
Didn't take a fidge out of it.
It's extremely robust. You can hardly strip it with a Stanley knife let alone damage it.
There's actually wool between the inner cores and the outer sheath.
Yes. I can't see any Regs that preclude this.We’ve pulled in a 185 cable just and realised that we need a neutral. It has 4 cores, brown, black, grey and earth. Can we use the earth as a neutral if we shrink wrap it with neutral sleeve and then run an earth separate?
AgreeNever heard of tri-rated flexible cable. There are rubber cables available in that size and if it is a long run someone has made a serious error.
It’s ok to sleeve the CPC in a multi core cable, but not if it’s a single core cable.Worth a read, I think:
Using Green/Yellow not as CPC - https://www.electriciansforums.co.uk/threads/using-green-yellow-not-as-cpc.35860/
Strictly speaking it would seem that over-sleeving is okay, but personally I'm on the side of those that would never do it - mostly due to the element of unexpected surprise that somebody maintaining the installation in the future might be confronted with.
It’s ok to sleeve the CPC in a multi core cable, but not if it’s a single core cable.