I have recently come across a situation whereby instead of running a main equipotential bonding conductor from the MET to the incoming water someone had instead ran a short bond from the MET to some copper pipe in the mains cupboard and clamped it and then placed a bond on the pipe near the incoming water (at the other end of the property) and bonded to the incoming water there.

Wander lead method states 0.02 ohms resistance.

I know this is not good practice but where does it say in the regs it has to be a continuous conductor and that you can't do it.
 
regs. specify that the bond to an incoming service should be within 600mm of the point of entry to the building, or as close as practicable. the scenario you describe might be fine as it stands, but when wet-pants comes along and cuts out some copper andreplaces it with that crappy DIY plastic crap, then you've lost your bond to the extarneous incoming service.
 
Obviously not a good idea as Tel says.
GN8 says that if the bonding is looped between services (e.g. MET to gas then gas to water) the the conductor should remain unbroken.
However 543.2 says that a bonding conductor can be a variety of different materials (many of which would require numerous joints) but do specify that the continuity of the bonding should be assured.
 
This could also be one of the occasions,where a visual,physical examination,could provide a better indication of possible issues,as 1x PFC is not available on the MFT :cyclist:
 
Guys cheers for the comments. I agree not ideal but I explained the scenario about the plumber coming along and cutting the pipe and the connection being lost. The section in GN8 certainly does say about the connection being unbroken however this reads as more of a 'recommendation' than a 'requirement' and describes a slightly different scenario.

I would never do it myself, I think it's poor practice but at the moment there is a bond. The resistance meets regulations blah blah blah. Would anyone give it a code when carrying out EICR?
 
What kind of warnings are there about not removing the pipe work, or replacing it with plastic?
Anything on the EIC, or any labels affixed along the pipe work?
 
The resistance meets regulations

The Regulations do not give a resistance to meet. If the resistance is that to be expected for the length and cross-sectional area of the cable you have then it is fine, otherwise something is wrong.
 
I thought it had to have a resistance of 0.02 ohms or less


Sent from my iPhone using Tapatalk
 
That's the bonding connection itself. Not the length of bonding cable. You can only work out what that should be by using the tables of resistance. Daz
 