munch88

Hi there.

I have very little experience wiring boilers and will be required to wire a Valliant 837 soon with an external thermostat (not sure on model)

I understand the thermostat controller can be wired as 24v or 230v.

On the wiring diagram, there is a connecton called RT (for 230v) which says it's for the thermostat. So does the thermostat controller require a permanent live and neutral from the load side of the FCU and a connection from terminal RT?

For 24v, does the thermostat just require a 2 core from the connections labelled as 24 RT?

Much appreciated
 
c0cd3bfd7155e62f623d13697bb967cb.jpg


is this the correct diagram munch88?
 
If wiring into the 24v input it is just 2 cables from the thermostat output into the 24v DC room thermostat input taking out the link, if 230v then it's just 1 into the 230v AC room thermostat connection, the bottom one, it's just a switch wire from thermostat, leave the 24v link in.
 
If you are using a 240 volt room stat then you need to remove the 24V link. If you don't then it will stay on constantly.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Valliant 837 Boiler Wiring?
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
munch88,
Last reply from
Johnmdc,
Replies
7
Views
9,781

Advert