M
munch88
Hi there.
I have very little experience wiring boilers and will be required to wire a Valliant 837 soon with an external thermostat (not sure on model)
I understand the thermostat controller can be wired as 24v or 230v.
On the wiring diagram, there is a connecton called RT (for 230v) which says it's for the thermostat. So does the thermostat controller require a permanent live and neutral from the load side of the FCU and a connection from terminal RT?
For 24v, does the thermostat just require a 2 core from the connections labelled as 24 RT?
Much appreciated
is this the correct diagram munch88?
If wiring into the 24v input it is just 2 cables from the thermostat output into the 24v DC room thermostat input taking out the link, if 230v then it's just 1 into the 230v AC room thermostat connection, the bottom one, it's just a switch wire from thermostat, leave the 24v link in.
If you are using a 240 volt room stat then you need to remove the 24V link. If you don't then it will stay on constantly.
Valliant 837 Boiler Wiring?
Central Heating Systems
Thread Tags
munch88,
Johnmdc,