hi all new here :) right so am upgrading my inverter set up in my work van i use this set up for tools and camping the new inverter going in is a

Victron Phoenix Inverter 12V 2000Va Smart what i am trying to work out is will i need to run it in to a 240v consumer unit RCD /MCB. my old ivereter just had plug socket on side i did run that with a rcd spur here is a link to what am getting Phoenix Inverter Smart 1600VA - 5000VA - Victron Energy - https://www.victronenergy.com/inverters/phoenix-inverter-smart
 
hi all new here :) right so am upgrading my inverter set up in my work van i use this set up for tools and camping the new inverter going in is a

Victron Phoenix Inverter 12V 2000Va Smart what i am trying to work out is will i need to run it in to a 240v consumer unit RCD /MCB. my old ivereter just had plug socket on side i did run that with a rcd spur here is a link to what am getting Phoenix Inverter Smart 1600VA - 5000VA - Victron Energy - https://www.victronenergy.com/inverters/phoenix-inverter-smart
The neutral output would need earthing to allow the rcds to operate in the consumer unit.Not sure if the
inverter could produce enough fault current to operate mcb,s.
Regards,S
 
Exactly, there's not much point having a box full of MCBs when your inverter has electronic protection at around 8A. As for what you will achieve with an RCD, you have to check the manufacturer's spec re earthing the neutral, and decide whether you are effectively running a single load from it and can therefore leave it floating as an IT source, or whether there is an advantage in making it TN if powering multiple devices outside the van for example.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
birighton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Victron Phoenix Inverter 12V 2000Va Smart inverter installation
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2
Unsolved
--

Advert

Thread statistics

Created
stevewah,
Last reply from
Lucien Nunes,
Replies
2
Views
2,050

Advert

Back
Top