hi all,

I have a situation where I would need to supply a 40kW installation from a Generator situated 300 meters away (not ideal). As this is a private LV supply up to 8% VD is permissible as per App. 4 Sect 6.4 in the BYB. However it then goes on to state that final circuits should not exceed public LV supply values of 5%.

The way I am interpreting this is that I can have up to 8% on my distribution cable to the origin of the installation(the DB) then a further 5% for final circuits.

This would lead to a possible situation of 348V L-L at the furthermost point in the installation if it did not contain lighting ccts.

Is this how others interpret it with respect to Section 525?

cheers,
 

Reply to Volt drop.................................................. in the UK Electrical Forum area at ElectriciansForums.net