Hello.
Im an enthusiastic diy'er and whilst finishing off a job that a local sparky came to do, i came across this 'fault' that i find a bit worrying.

My house is split up into to two section with separate consumer boards fed from henly blocks. When i was rerouting the earth cables for an additional supply i got a mild belt off one of them. Long and short of it after some testing, i found there was around 75 ish V present on the earth line. I disconnected everything and carried out an insulation test (500vdc) on the supply cable (16mm SWA - around 12m long) and all tested good except even with everything disconnected, i was still seeing 30v on the earth when live.

This is between the earth on that particular supply cable and the main incoming earth. Im presuming that this is an induced voltage? I know that this wasn't strictly safe as i essentially had a live supply with no cpc but i felt i needed to investigate this problem and i was as careful as can be.

Further testing on all the individual circuits from that board showed a few adding (around 8v) to the overall problem but i eventually traced the main culprits to the washing machine (40+v) and a dryer (15V). Is this normal? Obviously with all the earth lines connected this problem doesnt actually exist as any residual voltages would be 'drained' and would therefore be undetectable under normal circumstances so am i creating a problem where one doesnt actually exist? Currently my main concern is that the washing machine, being a cheap indesit, could be on its way out and would best be changed.
 
I know that this wasn't strictly safe as i essentially had a live supply with no cpc
I think that's your issue.
A lot of appliances leak to earth as a noise suppression measure, this is normal and wouldn't generally be enough to trip an rcd.
However it's very foolish to break an earth connection on a supply that's not otherwise isolated.
Even the gas guys have huge croco clips to connect across any gas pipes they break into in case of differences between the supplierss earth and the gas pipe/local earth.
 
Hello.
Im an enthusiastic diy'er and whilst finishing off a job that a local sparky came to do, i came across this 'fault' that i find a bit worrying.

My house is split up into to two section with separate consumer boards fed from henly blocks. When i was rerouting the earth cables for an additional supply i got a mild belt off one of them. Long and short of it after some testing, i found there was around 75 ish V present on the earth line. I disconnected everything and carried out an insulation test (500vdc) on the supply cable (16mm SWA - around 12m long) and all tested good except even with everything disconnected, i was still seeing 30v on the earth when live.

This is between the earth on that particular supply cable and the main incoming earth. Im presuming that this is an induced voltage? I know that this wasn't strictly safe as i essentially had a live supply with no cpc but i felt i needed to investigate this problem and i was as careful as can be.

Further testing on all the individual circuits from that board showed a few adding (around 8v) to the overall problem but i eventually traced the main culprits to the washing machine (40+v) and a dryer (15V). Is this normal? Obviously with all the earth lines connected this problem doesnt actually exist as any residual voltages would be 'drained' and would therefore be undetectable under normal circumstances so am i creating a problem where one doesnt actually exist? Currently my main concern is that the washing machine, being a cheap indesit, could be on its way out and would best be changed.
What readings did you get on your IR tests?
 
My house is split up into to two section with separate consumer boards fed from henly blocks. When i was rerouting the earth cables for an additional supply i got a mild belt off one of them.
one for those consumers must have been live ,did you not know to isolate the c/u.s before hand .
or did you think ,its ok :eek:
 
I would be doing basic dead tests ...
.. Not the diy hit and miss.

Why didn't the spark do this?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Suffolk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician
Business Name
Marine electronics

Thread Information

Title
Voltage Present on Earth Line
Prefix
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
59

Thread Tags

Advert

Thread statistics

Created
clanky,
Last reply from
dmxtothemax,
Replies
59
Views
8,500

Advert

Back
Top