Just had a call from an M&E client of mine and good mate asking to pick my brains.... large 3ph biomass boiler with (I assume variable speed) 1ph fans internally. Says he's got 230v L-N/E on the connecting plug but when the fan gets connected there's nothing on the internal fan connections. So I says "knackered fan or cable" - "Nope, changed it for a new one". So then I says "Well it could be a triac died on the controller board and all you're reading is a phantom voltage and it's disappearing under current draw". "Nope, I thought that too, changed the controller board as well". He's going back to his workshop to mess about plugging a fan directly to 230v just to check it, but can anyone think of any quick pointers?
 
Bad connection on a 230v isolator for the fan, if there is one.
Bad connection / failed motor overload.

When he finds the motor works on 230v direct he needs to go back the the source of the 230v, presumably in a control panel, stick a meter on the 230v and watch what happens.
If it stays 230v keep moving forward on the 230v line towards the fan and test again till he finds a point the 230v is disappearing.
 

Reply to Voltage to boiler fan 'drops out under load' in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
917
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
As title, call out to change a burnt out socket. The why? was over use of fan heaters. Quick Zs gave 1.26, something amiss. Did an Auto RCD...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock