I am currently doing a love job and found that the water pipes have 93.4v running through them? the problem i have is that this is intermittent, for about 5 mins at a time? so live for 5 mins then dead then live again? i wondered if anyone had advice before i take up floor and things. i thought maybe a problem with the boiler but as i was testing live we turned the boiler off at the spur and still had the volts, i have identified the circuit it is on, unfortunately the boiler is on the house ring. any ideas please? thanks in advance
 
93v when measured against what?
if you are measuring a voltage between an earth cable and a pipe, it suggests that either the earth cable is not bonded correctly or the pipe is not bonded to earth.

what is the method of earthing at the property?

I would start by finding out what the Ze is to confirm you have a decent earth to the property in the first instance.
 
Water can run through the pipes but volts can't run through anything. I take it you mean:
"I measured 93 volts between some pipes and something else"
If that other thing is a CPC or the MET or something supposedly earthed within the electrical installation, you've got two main possibilities:

a) The MET is earthed, but the pipes are not. Leakage from the installation to the pipes is raising their potential, possibly due to a disconnected CPC (in which case the leakage may be normal) or a fault from a cable to a pipe. Solution: find and fix the leakage source and / or missing CPC. Check whether the pipes should have been bonded anyway.

b) The pipes are earthed (or extraneous) but some or all of the installation is not. Leakage within the installation to the CPCs is raising part or all of the system to 93V above the potential that the pipes have found, but that's not immediately apparent as it's an equipotential and the problem is intermittent. However you should be able to catch it out with an abnormal N-E voltage soon enough. Solution: fix the broken CPC / EC / whatever.


A loose neutral connection by itself won't make pipes live or the CPCs live relative to the pipes. OTOH, a high resistance connection in a combined neutral/earth conductor could very well raise the potential of supposedly earthed bits by 93V w.r.t true earth. But then, the L-N potential would have to be 230-93 = 137V and I expect they would have rather obvious symptoms of flickering lights and appliances shutting down.

could be a phantom voltage

One would think the C/H system would have at least some earthed components so that it should not normally be floating, so this would fall into my category a) above.
 
Long story, but shortened here. As previously recounted, I came across a fault once, where plumber (son) got zapped when he touch copper pipes and bathroom wall. The wall was literally ‘live’; there was a voltage between wall and earth. Fault was intermittent.

The fault was eventually found; a previous owner of the property had nailed up some dado rail on the landing. One had nicked a strapper on two way for landing light. Note, on the landing, not in the bathroom.

Pooh happens. ;)
 
What are you testing this voltage with if I may ask? And where are you testing i.e. from the pipe to what?
Maybe switch everything off at the mains, then process of elimination one circuit on at a time might help?
hi mate, i'm using a fluke multi tester,and testing on the pipes to an earth source. i have identified the circuit and assume i will have to dig further under floors etc, but the it comes and goes every 5 mins just seems strange.
 
If it's not something turning on and off every 5 or so minutes, it may be as Midwest and a nail /screw through a cable but only just touching a pipe and breaking down the connection as soon as it's made.
Maybe water making the connection and boiling off.

If the fault is on a Ring, break the ring down into sections.
 
Turn off the power, run a temporary bond between MET and the pipe, restore power. 1 it will now be safe and 2 something may trip and give you a clue as to where the fault is.
 
I am currently doing a love job and found that the water pipes have 93.4v running through them? the problem i have is that this is intermittent, for about 5 mins at a time? so live for 5 mins then dead then live again? i wondered if anyone had advice before i take up floor and things. i thought maybe a problem with the boiler but as i was testing live we turned the boiler off at the spur and still had the volts, i have identified the circuit it is on, unfortunately the boiler is on the house ring. any ideas please? thanks in advance
Sirstan my advice would be for you to bond the pipe which will probably solve your problem
 
it could be a "ghost" ir induced voltage which the meter disharges when testing. . then 5 minutes later, it reappears.
 
hi mate, i'm using a fluke multi tester,and testing on the pipes to an earth source. i have identified the circuit and assume i will have to dig further under floors etc, but the it comes and goes every 5 mins just seems strange.
As Vortigern mentioned, it would be a good idea to use a drummond test lamp or an analog tester just to rule out Ghost voltage. I measured 200V once (on a 19 core cable) and went into panic mode before measuring it with the drummond and realising it was ghost voltage.
 
What’s connected to that circuit and when you say every 5 mins, do you mean that literally?
yep every 5 mins. it is like clock work, very strange unfortunately it is rewire-able fuses and the board needs updating but came across this problem and just wondered why it was intermittent before i cracked on with pulling boards up etc, the whole house is on one circuit lol and its a radial circuit to my shock so a lot of work to be done anyway. i now know that there is no main bonding to met and reading responses assume this is the reason? however it seemed quite high at 93.4v/ i am not a tester yet (defo doing that course this year)
 
yep every 5 mins. it is like clock work, very strange unfortunately it is rewire-able fuses and the board needs updating but came across this problem and just wondered why it was intermittent before i cracked on with pulling boards up etc, the whole house is on one circuit lol and its a radial circuit to my shock so a lot of work to be done anyway. i now know that there is no main bonding to met and reading responses assume this is the reason? however it seemed quite high at 93.4v/ i am not a tester yet (defo doing that course this year)

Why are you shocked to find a radial circuit? It's a perfectly valid type of circuit.

A lack of bonding will not be cause of this, but bonding could make the symptom disappear.
 
yep every 5 mins. it is like clock work, very strange unfortunately it is rewire-able fuses and the board needs updating but came across this problem and just wondered why it was intermittent before i cracked on with pulling boards up etc, the whole house is on one circuit lol and its a radial circuit to my shock so a lot of work to be done anyway. i now know that there is no main bonding to met and reading responses assume this is the reason? however it seemed quite high at 93.4v/ i am not a tester yet (defo doing that course this year)
When you say the Whole house is on 1 circuit and it's a radial, unsure of what you mean abd how you have come to this odd conclusion.
 

Reply to Volts running through water pipes in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
429
Hi All. Its been ages since I have been on here- Fortunately log in details stored on PC. I have just had a new boiler and 210 ltr unvented tank...
Replies
9
Views
1K
Hi everyone, I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's...
Replies
7
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
816
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
438

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock