thoughts on this,on drawings, water heaters are on a ring main circuit,dedicated to the heaters,there are 4 of these.
Listening to spark ninja this could prove a problem with the overloading & balancing of this ring.
Why would consultants decide on a ring ,instead,like the good old days,all heaters are cabled back.
 
If the water heaters don't store any water, they are of the instantaneous type and the On-site Guide suggests an allowance for diversity for such heater that results in the maximum demand being 32.6A. Given the UK power supply is often above 230V, I would say that this load is acceptable on a 32A RFC.

The designer could have made a mistake though and specified heaters that do store some water. In this case, the OSG's guidance is that diversity cannot not be applied. 2 x 32A RFCs would be required.
 
For all the schools we have done the consultants have always designed on radials.
Agree,really can’t see the point of this circuit.
It’s ridiculous,the tpn DB installed is a 6 way ie:18 circuits,the number of circuits on the drawing relates to 14 circuits,there are already a couple of extra circuits to be added,this all specified by consultants,kinda mad mad mad
 
Are they instantaneous or stored water type?

Depending where they are positioned in that ring could mean that one leg is being overloaded.
3kW fixed loads is not a good idea on a ring. They would have to be fused spurs with fuses running at limit, although you could probably argue load is determined and fit DP switches.
 
Always radials back to DB for me,other sparkies on site,attitude just do what’s on drawing.
That applies to everything including guessing positions on rooms,without asking for a detailed drawing,then when 2nd fix comes a knocking,it’s all wrong,& blamed on me.
 

Reply to Water heaters in new school in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
742
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hello, you all helped me out recently when we had a water leak (mostly in kitchen ceiling), and my landlord's contractor was saying the household...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock