Discuss What Filler for Consumer units etc in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Guidance note 4 3.8.1 advices "The intent of regulation 421.1.201 is, as far as is reasonable practicable, to contain any fire within the non-combustible enclosure...."
"The installer must seal all openings into the non-combustible enclosure...."
So what ever you use, it must be fire retardant in my eyes.
 
When I put cables into a new metal consumer unit, do I have to use intumescent glands to enforce the fire protection of the consumer unit?

No, the metal consumer unit is designed to encase a fire within it and restrict the likelihood that a fire may spread. Manufactures’ have carried out exhaustive tests on this issue and have found that the cable entry does not have to continue the fire rating of the consumer unit, for it to be effective. The only requirement is to keep IPXXD or IP4X on the horizontal surfaces (Reg 416.2.1) and IPXXB or IP2X on all other surfaces (Reg 416.2.2). Intumescent glands and sealants may be used to ensure the IP ratings are maintained, but they are not a requirement and existing methods of ensuring IP are acceptable.

Consumer units: a brief overview - https://electrical.------.org/wiring-matters/issues/59/consumer-units-a-brief-overview/
 
When I put cables into a new metal consumer unit, do I have to use intumescent glands to enforce the fire protection of the consumer unit?

No, the metal consumer unit is designed to encase a fire within it and restrict the likelihood that a fire may spread. Manufactures’ have carried out exhaustive tests on this issue and have found that the cable entry does not have to continue the fire rating of the consumer unit, for it to be effective. The only requirement is to keep IPXXD or IP4X on the horizontal surfaces (Reg 416.2.1) and IPXXB or IP2X on all other surfaces (Reg 416.2.2). Intumescent glands and sealants may be used to ensure the IP ratings are maintained, but they are not a requirement and existing methods of ensuring IP are acceptable.

Consumer units: a brief overview - https://electrical.------.org/wiring-matters/issues/59/consumer-units-a-brief-overview/

Good find, I'm not sure if this is compliments Guidance Note 4, or contradicts. Both are written by IET. Albeit different authors and neither are dated!

The complete text from Guidance note 4 17th Edition A3 is;
"The installer must seal all openings into the non-combustible enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables. Good workmanship and proper materials must be used and account must be taken of the manufacturer's relevant instructions, if any."

What is proper materials? I would argue flame retardant. But above is not conclusive.

I believe Wylex advise intumescent glands are required, but I'm not aware of any other manufacturers notes.

Does anyone have 18th Edition Guidance Note 4 to see if there has been an update?
 
Good find, I'm not sure if this is compliments Guidance Note 4, or contradicts. Both are written by IET. Albeit different authors and neither are dated!

The complete text from Guidance note 4 17th Edition A3 is;
"The installer must seal all openings into the non-combustible enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables. Good workmanship and proper materials must be used and account must be taken of the manufacturer's relevant instructions, if any."

What is proper materials? I would argue flame retardant. But above is not conclusive.

I believe Wylex advise intumescent glands are required, but I'm not aware of any other manufacturers notes.

Does anyone have 18th Edition Guidance Note 4 to see if there has been an update?

You could have a look at this vid, old by now (sounds crap at the start);

Fire protection: panel discussion 1 at the ELEX show in Harrogate - https://electrical.------.org/wiring-matters/issues/56/fire-protection-panel-discussion-1-at-the-elex-show-in-harrogate/

So as Andy said, just maintain the relevant IP rating, …….at the moment. You never know what laughs the IET might come up with next.
 

Reply to What Filler for Consumer units etc in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock