Here's the report, which doesn't look that bad...
There's some stuff that obviously needs doing, but I'm not so sure on a rewire now
P1
P2
P3
P4
P5
P6
I am in your neck of the woods. Are you busy tomorrow morning or next Wednesday morning for a second opinion?He's in my neck of the woods. I would not be surprised at a lack of earthing conductor. Most service heads never had the facility and there are plenty still without.
Still, the wrong codings ring alarm bells as to the legitimacy of the report.
Why no r1 r2 when he’s stated earth sizes of cables also why no ins res between L and N , looks more of a visual test he’s carried out here