Installing an over the range microwave, ran the (yellow) wire to the box, but where can I attach the ground and neutral wires? The one bus on the right is full, the second bus on the right is empty, but can I use it? Nothing else is attached to it.
 

Attachments

  • 20210418_130654.jpg
    20210418_130654.jpg
    432.4 KB · Views: 1,014
  • 20210418_130705.jpg
    20210418_130705.jpg
    366.9 KB · Views: 154
Installing an over the range microwave, ran the (yellow) wire to the box, but where can I attach the ground and neutral wires? The one bus on the right is full, the second bus on the right is empty, but can I use it? Nothing else is attached to it.
If that’s is your main panel you can hook up the grounds and neutrals to any one of the bars. If it’s a sub fed panel the neutrals have to be isolated from the grounds
 
Either I'm more confused than I thought, or we're at cross-purposes.

Am I not seeing, where highlighted, ground and neutral conductors connected together?

1619217105522.png
 
So if neutral isn't switched, then whatever the power company think about it, the electrons aren't going to be able to tell the difference between neutral and ground only combined to the point of entry of the service, and them being combined all the way to the distribution board, as in this case.
 
No it’s not, the neutral bar has an insulator on the bottom and is not an integral part of the panel, the ground bar doesn’t have an insulator
So, in terms of the panel construction, what are A, B, and C, and which have continuity?

1619282217755.png
 