I've been asked to install a coffee brewing machine which has come from the the USA. The plate says 2L/N/PE 230/400v
Any advice on how/if this can be wired into 3ph/1ph supply would be greatly appreciated. Many thanks
looking at that, 5600 watts,12.4A indicates a 400V supply, so seems as it needs to be connected across 2 phases of a 3 phase supply.
I was thinking that would probably be the case but was unsure about the phase offset with regards to 3ph being 120deg and the USA using 2ph at 180deg??
just a glorified kettle @ 100 x the cost.
Anybody watched Holmes on Homes? It's a Canadian show where people's homes are put right after dodgy builders have done work. From what I've seen, their domestic electrical system is a 2phase and neutral (L1 or L2 - N = 120v, L1 - L2 = 240v) so the 120v is for lights and sockets, 240v is for cookers, dryers, washers.
You had my attention at 'Coffee Brewer' - looks like Kevin is right as the 120v will use the neutral so at our voltage if used will use the neutral and provide the required power to make a nice cup of 'Joe'!
From this wiring diagram it would appear that the power supply for the control system needs 230V (from L1-N).
There are two 3kW heaters one has a supply from L1 and the other from L2.
Therefore I would suppose that if you have a 230V supply that can handle 30A then you could link the L1 and L2 or if you have two 16A single phase supplies you could share a neutral between them.
For a 400V system it would just be two phases of a three phase supply and a neutral that would work in the same way as the above single phase.
Perhaps.
Agree - until I saw the circuit diag I was thinking to follow the post #6 diagram and put L on one side, N on the other. But if it was wired as per post #6, how would the 24V /5V supply get energised ? (when the heaters were off for example)