Discuss Would you extend this RFC? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hi - as per Dave.
If the extension has heating that doesn’t rely on this circuit likely the biggest new load will be a vacuum cleaner :) .
I agree too as as long as your ZS is within the the limits of the installation methods .
If I remember correctly 100mtr square was the limit of an RFC without calculation.
The cable length calculation I used was
Vd = L x Ib x (mV/A/M)/ 4 x 1000.
So VD = 113 x 32 x 18 /4000 = 16v
I’ve already divided the end to end value by 4. This is how I was taught to calculate volt drop at the mid point on a RFC.
Does this look correct to you?
I wouldn't use 32A as the design current.
De-rate it to 20A RFC if possible, VD would be less than 5% if using the full 20A load but as the main usage would be the kitchen RFC I doubt the remainder would use 20A (unless electric heating!). Higher max Zs value too!
Reply to Would you extend this RFC? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Well....wiring in a 1750s thatched cottage attic, not wiring made from thatch 🤪 One we have been letting for over 20 years (as well as enjoying...
4K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
On a couple of recent EICRs I've run into FCUs on a RFC, then 1.5 or 1mm to several lighting points and would be interested how people would note...