So I have a client who requested a towel rail fitted at the end of the bath on wall, opposite end from shower (fixed) and taps and so is right bang in zone 1.

Never fitted any before unless in zone 2 at least, OSG seems to okay it but through flex outlet, but I'm thinking it would be really open to abuse of water splashing possibility into flex outlet hole.

Anyone be happy to fit that ?
 
Not through a flex outlet I wouldn't. Not suitable for the environment.

Fitted a zone 1 located towel rad before, but the rad came flexed and sealed, the flex ran through the tiles and under the bath, all sealed up by the plumber, and the connection was in the next room at a FCU. I was happy with that.
 
The towel rail will be fine fitted in zone1 providing manufacturers instructions allow. Do not put flex outlet in zone 1. Cant you punch flex through wall or suitably extend to a suitable location? Is 30mA rcd protection provided?
 
Thanks guys, only option I thought about was like that and get plumber mate to seal around tightly with a mastic appropriate for the job and run to cupboard way outside on landing where fcu is ready. So great advice, cheers.
 
The towel rail will be fine fitted in zone1 providing manufacturers instructions allow. Do not put flex outlet in zone 1. Cant you punch flex through wall or suitably extend to a suitable location? Is 30mA rcd protection provided?
No rcd in place yet as old Starbreaker CU so will either get one in there or maybe rcd spur.
 

Reply to Zone 1 dual fuel towel rail ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, a friend has asked about fitting an electrically heated towel rail in their bathroom. The location is on the wall opposite the bath in a...
Replies
2
Views
4K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hi. I am fitting an electric towel rail in Zone 2 - it is IP55 rated so fine there. The flex coming out of it I have a few options - There is...
Replies
9
Views
8K
Hi guys and girls, So im fitting a new ring final circuit (I did advise a radial) in a newly built extension. the least disruptive way of feeding...
Replies
13
Views
3K
I have a customer who has questioned/insulted my price on completion of work plus extras. Basically I was asked to wire an electric shower, it's...
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock