Can someone explain this to me?

The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
 
Zs is the earth fault loop impedance of a circuit, Ze is the earth fault loop impedance external to the installation which makes up part of Zs. So Zs=Ze+(R1+R2).
 
They are both earth fault loop impedance

Ze is the loop external to the installation.

Zs is the loop to the accessory, including any parallel paths.

edit,

@westward beat me to it.
 
Zs is the earth fault loop impedance of a circuit, Ze is the earth fault loop impedance external to the installation which makes up part of Zs. So Zs=Ze+(R1+R2).
It would be nice if this was explained in the book instead of them just using the exact same terminology for both.
 
The external value Ze is your starting point for any design, then you can compute a circuit's expected Zs from Ze + R1 + R2 as @westward10 said and you know it should not be more than that, though it might well be less if there are parallel paths (for example, lowering the effective Ze via bonding to shared metallic service pipes). From the circuit (which could be a sub-main) you can then check your disconnection times are being met.

As @Rockingit points out, you also see Zdb which is "similar" to Ze but for circuits coming off a board/sub-board. From a design point of view you would compute Zdb as above (i.e. Zdb = Ze + R1sub-main + R2sub-main), and then for all circuits off it do the same again.

In practice for larger existing systems any new work is likely to use measured values as it might be too disruptive to isolate the whole installation to check Ze (if not well documented). Then parallel-paths would be included which is not always a good idea as they might be removed without notification (e.g. metal water pipes replaced by plastic).
 

Reply to Zs and Ze - both called 'Earth Fault Loop Impedence'? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
483
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
683
Confused as to what the earth fault loop is. I'm aware it's the path that fault current takes (Line-Earth) but how many times does fault current...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock