Discuss Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net
Morning, just checking a lighting circuit on a house, I have the main earth disconnected and still get a zs reading of 2.2 ohms. No evidence of an earth spike and bonding goes direct to henley block.
Any suggestions why this could happen??
pics. would help. is you 2.2.ohms a reading from the bonding?
I don't understand either. And why would you expect the CPC to be insulated from earth throughout the installation? It could take any value from infinity to zero without indicating anything abnormal. I can see why it might be useful to know for forensic analysis but not for normal testing.
So to answer why I had the circuit energised with the main earthing disconnected..
The lighting circuit connected in board had no CPC so I checked the Zs at a ceiling rose.
I had a reading of 2.2 ohms so I then tried to find out where the earth was coming from.
I disconnected all the CPC's from the other circuit in the board, checked Zs again and still had 2.2 ohms.
Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
You can’t make an omelette without breaking a few eggs.....
Why do this as a live test when that means doing something as stupid as energising the installation with the earthing conductor disconnected?
Electricians are supposed to understand the fundamental principles of electrical safety!
Reply to Zs reading with main earth disconnected in the UK Electrical Forum area at ElectriciansForums.net
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Been asked to do some rewiring, and have said needs upgrade of consumer unit really Main question is regarding earthing - Zs reads at 0.45 ohms...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...