Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
 
Disconnecting the earthing conductor for an energised system isn't the wisest thing to do. You are better to try dead tests by way of a continuity tester.
 
Many years ago I used to disconnect the main earth and carry out various tests to help me understand parallel earths in electrical installations.
Done lots of other experimental testing in a controlled environment...
You can’t make an omelette without breaking a few eggs.....
 
Just try and eliminate things and to see if I was picking up earth from elsewhere I then disconnected the main earth and still had a reading of 2.2 ohms.

Why do this as a live test when that means doing something as stupid as energising the installation with the earthing conductor disconnected?

Electricians are supposed to understand the fundamental principles of electrical safety!
 
Why do this as a live test when that means doing something as stupid as energising the installation with the earthing conductor disconnected?

Electricians are supposed to understand the fundamental principles of electrical safety!
Thanks for that post really helpful!
 
Are you doing a L-N Zs or L-PE Zs as I know my kewtech can do both. What system is it? i.e. TN-C-S or?
 
So you've got a circuit with a CPC present in at least one fitting, but no CPC present at the DB, and you want to find out where that CPC is getting its earth from, to decide whether it's trustworthy?

If it were me, I'd turn the board off, maybe separate out the CPCs, null out a nice long wander lead, clip the end of it on the CPC and probe various likely contenders around the house with the meter on low ohms, to see which gives the lowest reading and hence is the likely tap off point. I can't see any advantage investigating this live, but many disadvantages.

Or, since it's at least a bit of a bodge, maybe a lot of a bodge, declare the circuit CPC-less and treat accordingly.
 
Zs is line to earth external impedance, it stands for nothing else.
I understand that but my MFT has those two choices. The KT63 has a piggy back lead that you place the earth lead into to test across L-N I am not truly sure of the purpose of this but there it is. Perhaps you could shed some light on that?
 
Of course there is PSCC and PEFC which I also understand before you go there. I know I should have said loop test. Or PFC PSC even
 
Last edited by a moderator:
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.
 
Depending on circumstances, main earth may need to be disconnected to verify certain fault conditions..
All comes down to knowledge, understanding what is going on and being in control of the location.

What conditions would they be?
I can't think of any reason to have an installation which relies on ADS energised without its connection to the earthing system.
 
Of course there is PSCC and PEFC which I also understand before you go there. I know I should have said loop test. Or PFC PSC even

Yes it is a loop impedance test which is carried out.
PFC and PSC are not tested or measured, they are calculated by the meter based on the loop impedance and voltage measured at the time.
 