Hi I have been looking in to wiring up a garage which has a exsiting swa cable running to it just wanted to run this by some of your for your opinion . Supply is from 20a rcbo using 3 core 2.5mm swa into isolator
In the garage there is to be 2 power sockets and 1 lighting circuit with 4 florescent luminaries this will be connected to a small rcd cu with a 6A mcb for lights and 16A mcpvfor power there are also no ECP .
I am using a design current of 17.A 16A for the radial circuit which is the rating of the mcb and 1A for the lights rated at 0.25A each
so the swa cable Vd is 18mv/a/m so 0.018×17×20 =6.12v
lighting Vd 1.5 mm t/e 29mv/a/m so 0029×1×10 =0.29v
power 4 mm t/e 11mv/a/m so 0.011x16x10 = 1.76v
giving a total from supply to end of light circuit 6.41v
which is less then the max of 6.9v or 3%
And total for power of 7.88v which is less then 11.5v or 5% given
I know this is on the limit but providing new and upgraded swa to garage is a nightmare and if it's there would like to use
can anyone find a problem with this. Any help would be great