Discuss working out volt drop in the Electricians' Talk area at ElectriciansForums.net

D

darren1981

Hi I have been looking in to wiring up a garage which has a exsiting swa cable running to it just wanted to run this by some of your for your opinion . Supply is from 20a rcbo using 3 core 2.5mm swa into isolator
In the garage there is to be 2 power sockets and 1 lighting circuit with 4 florescent luminaries this will be connected to a small rcd cu with a 6A mcb for lights and 16A mcpvfor power there are also no ECP .
I am using a design current of 17.A 16A for the radial circuit which is the rating of the mcb and 1A for the lights rated at 0.25A each
so the swa cable Vd is 18mv/a/m so 0.018×17×20 =6.12v
lighting Vd 1.5 mm t/e 29mv/a/m so 0029×1×10 =0.29v
power 4 mm t/e 11mv/a/m so 0.011x16x10 = 1.76v

giving a total from supply to end of light circuit 6.41v
which is less then the max of 6.9v or 3%
And total for power of 7.88v which is less then 11.5v or 5% given
I know this is on the limit but providing new and upgraded swa to garage is a nightmare and if it's there would like to use

can anyone find a problem with this. Any help would be great
 
Why calculate for both circuits when you are only supplying 1 cable, calculate the VD for that cable that will be sufficient
 
what will the sockets be used for? if no heating appliances,welders, etc., then you'd be hard pushed to pull >10A
 
Also, you can calculate each circuit in sections if you wish - so if you have four light fittings along a radial circuit at 10m intervals, the first 10m is calculated at full load, the second at 3/4 load, the third at 1/2 load and the fourth at 1/4 load (assuming all loads are the same).
 
Hi I have been looking in to wiring up a garage which has a exsiting swa cable running to it just wanted to run this by some of your for your opinion . Supply is from 20a rcbo using 3 core 2.5mm swa into isolator
In the garage there is to be 2 power sockets and 1 lighting circuit with 4 florescent luminaries this will be connected to a small rcd cu with a 6A mcb for lights and 16A mcpvfor power there are also no ECP .
I am using a design current of 17.A 16A for the radial circuit which is the rating of the mcb and 1A for the lights rated at 0.25A each
so the swa cable Vd is 18mv/a/m so 0.018×17×20 =6.12v
lighting Vd 1.5 mm t/e 29mv/a/m so 0029×1×10 =0.29v
power 4 mm t/e 11mv/a/m so 0.011x16x10 = 1.76v

giving a total from supply to end of light circuit 6.41v
which is less then the max of 6.9v or 3%
And total for power of 7.88v which is less then 11.5v or 5% given
I know this is on the limit but providing new and upgraded swa to garage is a nightmare and if it's there would like to use

can anyone find a problem with this. Any help would be great


Looks generally OK. Not looked up the VD figures. A few comments:

I'd be surprised if you really have 10m of final circuit for the lights. Certainly it won't all be carrying the full load of the circuit. However, in this case, refining the calc won't make much difference.

Have you taken power factor into account with the lights? It's not much current anyway, but just for completeness.

Why are you using an RCD board in the shed when the distribution circuit is protected by an RCBO?

Why are using 4mm² for the socket circuit on a 16A MCB?

With this sort of question, it's always worth stating the earthing system in use.
 
It's suppled from a pme system
rcbo at supply end and rcd at garage end but over the top but it's not going to give any nuss tripping.
4mm fro radial (got in in the van )
 
What has PME go to do with RCDs at both ends ?
he is a trainee mate with 8 posts.

to op ask your mentor what they would recommend but you shouldn't be designing it yet because there are errors already and you might make a hash of it.

before you do this answer a couple questions first.

ccc of 2.5 swa,twin etc
why do we use rcd's?
why is having two rcd's in series a bad idea?

in a TT system what is the difference between the upfront rcd and a 61008?
 
Supply SWA connected in to switch fuse. RCD/RCBo's at the board!

Pointless having an RCD both ends unless the upstream one is S type. Not really necessary with PME?

Any thoughts on this anyone?

That is what I was getting at, the SWA does not need RCD protection on a TN system, two 30mA devices won't discriminate anyway, I was wondering why the OP brought PME into a (possible?) reason for the supply RCBO ?
 
That is what I was getting at, the SWA does not need RCD protection on a TN system, two 30mA devices won't discriminate anyway, I was wondering why the OP brought PME into a (possible?) reason for the supply RCBO ?
he is a trainee, i wouldnt be suprised if he is a first year

it sounds like a homework question, if it is its in the wrong section


he mentions mv/a/m on basic domestic circuits so its homework, why would you need to work this out when it gives you all that info in bs7671 and onsite guide if we wanted it
 
I wasn't having a go at him Shanky :) , just curious as the thinking behind it that was all :) , I must admit that I had dark thoughts of someone thinking a source/supply RCD may somehow negate possible bonding issues with PME, as I have heard this before from someone who should have known better :)
 
It's suppled from a pme system
rcbo at supply end and rcd at garage end but over the top but it's not going to give any nuss tripping.
4mm fro radial (got in in the van )

Over the top is one one thing but wasting money and having no discrimination of 2 rcd in series thus does not comply to regs is another, yes its not going to give nuisance tripping par' ce but its poor design from a professional all the same.
 
No, it won't. Or am I missing some of what you missed?
 
I have thought for a moment and I cannot see why an ordinary RCD test button would trip an upstream RCBO. Pray tell...
 
just out of interest, can anyone quote a reg. that forbids 2 30mA RCDs in series?
 
I have thought for a moment and I cannot see why an ordinary RCD test button would trip an upstream RCBO. Pray tell...

Right, I have had a thought :), and it seems maybe you are correct and I was wrong for this scenario being that the RCBO is upstream and the RCD is downstream, however if the RCBO and RCD were the other way around then it trips both devices for some reason, maybe something to do with the functional earth on the RCBO ?

I know this as a fact because I once was testing a custom built SP DB (by the firm I as working for), and all of the test rigs were in use so I used a normal socket outlet and "widow maker" lead to power this DB up to check the metering etc., anyhow I accidently caught one of the test buttons on one the many RCBOs fitted to this board and promptly tripped out the supply RCBO for this supply too, the howls of protest from a co-worker whom was using a computer powered from this supply revealed this lol :)
 
Reg 1: Use Common sense.

or it'll be something out of Chapter 3 about discrimination.

yes. i know, but was seeking a specific reg.

531.2.9 only asks for discrimination between RCDs when it is necessary to prevent danger.
 
I was always taught that the test button mechanically tests the device. I'm not sure about RCBO's.

well yes to an extent, it checks the electro-mechanical aspects out, the test button usually switches a resistor from the incoming L terminal to the outgoing N terminal so it checks the trip coil operation too.
 
he is a trainee, i wouldnt be suprised if he is a first year

it sounds like a homework question, if it is its in the wrong section


he mentions mv/a/m on basic domestic circuits so its homework, why would you need to work this out when it gives you all that info in bs7671 and onsite guide if we wanted it

Sounds like he wants to do the job because he's applying for elesca registration in another thread he started.
 
well yes to an extent, it checks the electro-mechanical aspects out, the test button usually switches a resistor from the incoming L terminal to the outgoing N terminal so it checks the trip coil operation too.

That makes sense, but wouldn't cause an upstream device to operate as it only diverts current to neutral so no imbalance would be detected on the other device.
 
That makes sense, but wouldn't cause an upstream device to operate as it only diverts current to neutral so no imbalance would be detected on the other device.

Hence my earlier reply to Lucien ;) , I am not sure why the RCBO tripped out the upstream one that I did at work though, but it did.

I might tomorrow fit my spare RCD that I keep, to a plug and lead , and see if it trips out the house RCD lol :)
 
My downstairs sockets at home are fed from a rcbo and I spurred a outside rcd socket off this circuit, now every time I use the outside socket I always push the test button and it has never tripped the upstream rcbo.
 
My downstairs sockets at home are fed from a rcbo and I spurred a outside rcd socket off this circuit, now every time I use the outside socket I always push the test button and it has never tripped the upstream rcbo.

I wonder if it only happens with an RCBO downstream ?, as I said maybe it was due to only certain types or possibly with the functional Earth when this is present.

I originally opened my mouth based on my earlier experience without thinking , then I thought about it and came around to Luciens way of thinking. :)
 
some one asked what earthing system was in place that's the only reason there shouldn't be any bonding issues as there is no extraneous conductive parts. two rcd in line yep I agree the only reason that the rcbo is there is because it was is all ready in place. what would be best the rcbo at source or rcd on garage board???
 

Reply to working out volt drop in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Why is this still a thing, just done a quick calculation with the TLC volt drop calculator and if its a non lighting circuit the recommended size...
Replies
3
Views
946
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I'm getting a little confused about volt drop and 24v. I want to fit an LED strip light. 8m of lights 7w/m. It would be easier to have the 24v...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock