Hi

I am probably going to sound stupid asking this question but here goes. I have just bought a new LAP voltage tester. when testing my plug sockets using a socket test connector I am getting a reading of .410V. Now this is where I will probably sound stupid but I was expecting around the 230V as is the voltage provided in uk houses. Can someone put me right please.

sonia
 
Hi

I am probably going to sound stupid asking this question but here goes. I have just bought a new LAP voltage tester. when testing my plug sockets using a socket test connector I am getting a reading of .410V. Now this is where I will probably sound stupid but I was expecting around the 230V as is the voltage provided in uk houses. Can someone put me right please.sonia

this is probably your problem lol.
 
Is that my stupidity or the lap is crap. I have a megger multi meter. I literally just wanted the voltage tester for completing safe isolation but the readings have thrown me.
 
According to GS38 this equipment meets the requirement. I need it for monday, screwfix is the easiest place for me to go. Would you recommend I just upgrade to the kewtech voltage tester.
 
why is it crap? you isolate and then using a voltage indicator carry out the 10 point check.
 
why is it crap? you isolate and then using a voltage indicator carry out the 10 point check.
that isnt a voltage indicator its a voltage tester.

gs38 covers the leads mate.

get a martindale indicator they go on forever and are reliable

martindale-vi13800_1.jpg


a lot of lap gear is crap
 
For safe isolation, you want an "Approved Voltage Indicator", plus (ideally) a Proving Unit.
A voltage indicator will prove voltage is or is not present, safe isolation is achieved by competance as well as testing equipment.
 
I wanted to be sure that the voltage meter was working correctly. I will be going to get a proving unit before monday, lesson learnt.
 
A voltage indicator will prove voltage is or is not present, safe isolation is achieved by competance as well as testing equipment.
Yes and it proved voltage was present I was just confused by the reading. It was not what I expected.
 