It is possible for an RCD to trip if it is subjected to a high electromagnetic field from outside the RCD such as caused by a short circuit, but the situation has to be right for this to occur.
In general if an RCD trips randomly on a circuit that has been tested as well within limits on all results then there is an intermittent earth fault on a connected item of equipment.
 
I had a customer had loads of stuff in their home, it was very very packed. The customer had pushed something onto the isolator for a washing machine.This held the switch in 'mid postion', it was neither on or off which caused enough arcing to trip the RCD. So no you dont need an earth fault to trip an RCD, as said you need an imbalance. 99.9% of the time an RCD trips due to earth fault
 
No, he means high. If it was low then tripping would be expected. He is asking if a circuit with a high IR etc would suffer nuisance tripping
I don't know how but I read that totally wrong....I was assuming under fault conditions!
 