Hi all

i have a customer who would like me to install 8 of these up/down outside wall lights all round the house, went and had a look at the job and the house is fully rendered and immaculately decorated throughout!!

Initial thoughts were swa around the bottom of the house into adaptable boxes then conduit/flex up to each fitting, trouble is the fittings are surface mount with cable entry through the back so I'm worried it'll look ****e

anyone done anything similar?
 
Any surface work above or below the fitting will look awful as it will be fully illuminated by the light.
What's wrong with running the cables under the upstairs floor as normal then down the cavity to the required height?
 
or fit the lights just above ceiling height, if that's acceptable.
 
Cheers chaps, the back half of the house is single storey so no loft space/floorboards.

I did think that the light will illuminate he cable below, trouble with clients buying their own gear I guess!!
 
Walk away from the job if you can't do as mentioned above using cavity or ceiling void height anything else would look shabby unless they are prepared to patch up the render and redecorate outside
 
Cheers chaps, the back half of the house is single storey so no loft space/floorboards.

I did think that the light will illuminate he cable below, trouble with clients buying their own gear I guess!!

Where are the lights going to be mounted on a single storey building? Up/down lights will look even more ridiculous than usual.

For the single storey part they'd be better off with the ones which just point downwards, then clip the cables tight in to the eaves
 
then down the cavity...
Can you tell me how you would protect the cable and stop it touching both walls bridging the gap for wet etc...

I have to say Dave, I thought you would be the last person to suggest running cables down a cavity...
 
Can you tell me how you would protect the cable and stop it touching both walls bridging the gap for wet etc...

I have to say Dave, I thought you would be the last person to suggest running cables down a cavity...

Protect the cable from what?
It'll be running downwards from inside to out, the same as any cable drilled through a wall. It's no different from all those wall ties that link the skins together.
Electricians have been dropping cables down cavities since long before I was born, and it was just something I was taught as an apprentice.
 
Take these regs for example as to why you should not do it...

522.8.1: Damage to cables during installation
Obstructions in cavity e.g. metal wall ties, mortar projections, create a risk of unseen damage.

522.8.4: Strain on cables lacking support.
Long unsupported vertical drops may put strain on conductors.

522.5.3: Materials liable to cause mutual or individual deterioration.
Expanded polystyrene sheets, granules or foam used in buildings for insulation if comes into contact with thermoplastic (pvc) cable sheathing, plasticiser can migrate from the thermoplastic to the polystyrene.

523.7: Cables in thermal insulation
Thermal insulation installed in cavity walls during or after construction, the cable current-carrying capacity is to be taken as half the clipped direct (Reference Method C) rating unless more precise information is available.

522.9.1 and 522.10.1: Presence of flora and fauna
 
Also just to add to that

NHBC Requirements
It is noteworthy that the National House-Building Council states, in Section 8.1 - S2 of NHBC Standards, that no cables other than electricity meter tails are to be located in the cavity of an external wall. Where meter tails do have to pass through the cavity, however, this does not preclude the requirements of BS 7671 referred to in this topic having to be met.

Building Regulations
Building Regulations 2000, Approved Document C, 2004 Edition, Section 5: Walls, paragraph 5.13 b Cavity external walls, requires, amongst other things, that a cavity external wall is at least 50 mm wide, and the cavity is to be bridged only by wall ties or by cavity trays provided to prevent moisture being carried to the inner leaf.

A cavity is intended to provide a gap to prevent water penetration. Cables could bridge this protection if they touch both the inner and outer leaves of a cavity wall. Furthermore, the cables could provide a route for water to drain directly into accessories, with potentially dangerous results.
 
Best not fit any outside lights or sockets or meter tails then let's face it bridging cavities happens, I agree not best practice but not uncommon, main factor is thermal nsulation
 
I have no issues in running cables through a cavity wall with the correct protection such as a bit of pipe to feed to the cables in, but would never run cables down a cavity, not unless put in during the construction of the wall and suitably protected etc.
 