Guest viewing is limited
Been asked to install 3 X sockets 1 X light 1 X PIR light into a summer house. The building is 45 mtrs away from the house and I'm unable to wire back to the board. My plan is to take a fused spur of the ring and use a 4mm SWA to feed the summerhouse. In summerhouse I intend to install a 2 way garage unit for the circuits. My query is would you use a RCD main switch or a normal isolator. The ring Is RCD protected already. My other question is this a minor works or installation certificate. My thoughts are minor works as it is an alteration to an existing circuit.
Thanks.
Have you worked out the Volt drop for the run PAD? 45m sounds quite a long way. Also, I know it's perfectly acceptable to take a spur for shed power but it would be better to have a seperate MCB.
There really isn't any point in having 2 rcd's on the same circuit, it's already got RCD protection from the main CU.
I was about to say minor works cert (MWC) as you're not adding a new circuit, but you are installing a CU... so it's notifiable and would need an electrical installation cert (EIC)... I think... tired...someone else will confirm!
Done a calc for volt drop 4mm is ok, did think of using 6mm but thought it was a bit over the top as it just running a fridge and a couple of lights. Got a log burner in there so not going to be used for heat. Did think of just using a double pole switch and FCU for the lights.
For what it costs I'd just stick a bigger cable in.
the spur element of it only needs a minor works but the new CU needs an EIC, however, you should be able incorporate both into the EIC.
The supply is only going to ha e a 13A fuse in it, so whatever you put in the garage unit will need to be smaller for them to be of any benefit I suppose, Hager do MCBs starting at 1A.
What is the point of installing a CU in this shed? If the supply is already fused at 13A then the MCBs won't be achieving very much at all!
This smacks of very poor design!
Your right there is no point in fitting a CU, overthinking it as usual. Just stick with a FCU at the house and just use a 20 amp switch at the Summerhouse to isolate and fuse the lights down. Wants going back to the board really, but no way to it without major alterations.
A 20A switch to isolate and fuse the lights?
If it needs major work then do major work, bodging it because you don't want to do it properly is hardly a professional approach
Will your installation be safe then???? as for certificate you are an electrician, should you be asking these question??
Unfortunately in the real world Dave there's a point where cost can outweigh the benefit and you have to compromise on how you do the job to keep it affordable - obviously not cutting corners with safety or contravening regs but a 13amp supply is usually perfectly adequate for a summer house where electric heating isn't required - I have 3 sheds running off one FCU at the house, never blown the fuse yet. Lights simply run from seperate FCUs C/W 3 amp fuses. :smiley2:
Don't take this as criticism of the OP, it's not intended to be, but I cant help but wonder at such a simple installation confusing an NICEIC DI......Maybe the NICEIC need to have a look at the level of experience required as an approved DI.
If I was really cynical I might think just for a moment that all they are interested in is the fees.....surely not?
I am also not going to try to upset the OP, all I will say is the whole design is wrong and IMO another good think about the whole installation should be considered.
Still too many posts that come across as rather hostile on here IMO. :(
You're reading them wrong.
It is perfectly reasonable for a forum of professional electricians to question the installation, design, and certification of a person who is supposed to be entirely competent in carrying out the said tasks and who is asking for advice and criticism of the proposed works.
I think that the issue of competency in the workplace in our industry, and making sure that the question asked is guided in the right direction to produce a safe and compliant job is of far greater import than worrying about inferred tones on an internet forum.
What you do in your own house is up to you, but if you sell that to a customer as an installation design then that's a different matter.
I don't see how spurring from a ring circuit to feed a summer house gives good segregation of circuits or minimises the potential disruption in the event of a fault.
I understand your point Andy but there's a lot to be said for guiding people rather than scaring them away never to seek advice again. The issue of competency in our trade is a very thorny one indeed, with monotonous regularity I come across work by 'registered' electricians which is rough beyond belief , they generally put all the right stickers on though.
My gripe is not with the OP, (who clearly has taken the correct course in asking for advise which proves he wants it to be right)....but with the NIC. Personally I don't think it's unreasonable to expect an installer registered as competent by the NICEIC to be able to design an install like this without assistance
All I'm saying is that practicalities need to be considered, in my case it was the simplest safe option, much easier than getting a dedicated supply right round the other side of the house with the associated disruption. The only way to achieve truly minimal disruption in the event of a fault is exclusive use of RCBOs and in my experience 60-70% of customers don't see the benefit and don't want the additional cost.
To be fair to all in this thread including the op, the questions are pretty basic and anyone undertaking the work as a professional tradesman should know the answers to those questions and if they don't they shouldn't be working alone, That's not a dig at the op but a valid point. As for member replies to be fair I don't see anything nasty or argumentative just genuine concern, sometimes text can come accross the wrong way but is not meant that way. A couple of members have raised concerns about the installation method and design which for me is what the forum is here for.
Have tried to think of another way to do it. Can't get back to board as it is at the other side of house, has double height hall way with no way across. Going around the outside is not an option either, so going off the ring seems to be the only option. My plan is to have a switched fused spur at the house end and a 20 amp switch in the summer house to provide a local means of isolation if required, then fuse the lights down to 5amp. Not ideal but cost effective, as long is the test are within regs. Not ashamed to admit I've retrained was TV engineer for 15 yrs, put my self through night school for 2 years to get my qualifications, still learning aiming to do my NVQ.
Oh yes, as long as the tests are within regs then it must be ok!
Don't worry about the reg which requires good workmanship or any other nonsense like that, if you start paying attention to that then you'll be in danger of taking pride in doing a good job!
Have not taken any offence to the criticism of design. That's why I asked the question, guys on here have far more experience. Not had the advantage of an apprenticeship, but did my city and guilds level 3 as a service engineer so do no a thing or two about ohms law etc. Have done my 2395/2394 as well. What lets me down is the experience of the best way of tackling certain jobs.
Good for you Mate, perhaps if you had mentioned you were still learning you might have got a more sympathetic response, certainly my reply would have been less caustic.
Maybe the OP should be allowed in the trainee section so he can post in their and get useful advice and confirmation from the contributors out of the way of prying eyes and the general public?
I used a similar system to the OP a few months back. In all fairness, I had nothing to do with the design of it. A girl at work (painter) had just had a summer house built and wanted power, she'd had a piece of 4mm armoured that had been down years and wanted connecting. It was also spurred off the ring via a 13a FCU. I just put a 20a isolator as it entered the summer house, ran 3 sockets, and fused down the lighting to 3a.
However, as stated, I hadn't designed the whole lot, and was merely working with existing. All tested out fine, and I saw no major problems with the operation of it.
Emm, it's all too easy to say this an that, not the best design, but nothing wrong with it, providing the ccc an ocpd/ testes are all in order,it is very difficult out there in the real world,if the job might be jeopardized all because of price, I absolutely hated battling with clients, you gave them the best solutions an advice, an them trying to get you to work for next to nothing and the cheapest way, in an lot of ways thank goodness for newer regs= rcd's split boards rcbo's. part p ( had to throw that in tee hee)
Not everyone knows the answers to everything Davesparks we're not all blessed like yourself :tongue3:
Nothing wrong with asking others better methods, even if you do know the answers, confirmation is helpful, and sometimes we ask questions without thinking them through!
Hostility is now in the other forum, let it stay there.
I really don't have a problem with this sort of installation. I've just quoted to run a supply to a tiny summerhouse. They want a double socket to plug in a small tubular heater to take the chill off plus a radio and a couple of wall lights. No problem taking this off a socket circuit via a SFCU. Max load is probably going to be less than 3A.
On the other hand, I'm doing two 'garden office' supplies this week. Both on 32A dedicated circuits.
I really don't see the point in replies like this, and the forum is risking going back to it's 'unfriendly' nature which it had a few months ago.
What is wrong with an FCU on the ring feeding a summer house with minimal load. Potential disruption is minimised, fusing is appropriate, RCD protection is in place. He's already looked in to going direct back to the board and can't so at least he's considered it.
Daz
Daz
Alsager, Cheshire
Supply to summer house.
PAD66,
DPG,