...well,it's a very common abbreviation,of a device the OP said he was short of...first letter;means "validated",second is the medium,scale or type of an electric characteristic,third is the description of the device role.

And,even on me hols,i always have one to hand:goofy:
 
I live about 10 miles from Hayle, weather's not great for a holiday at this time of the year though. :p

...Now that is a PROPER Cornish understatement!

Got family down this end,so regular visits are made...some Easters are sunbathing on the beach at St.Ives...others are spent chasing 47Kg LPG bottles around Gwithian Sands....but no problems launching the kids kites this year :lol:
 
...well,it's a very common abbreviation,of a device the OP said he was short of...first letter;means "validated",second is the medium,scale or type of an electric characteristic,third is the description of the device role.

And,even on me hols,i always have one to hand:goofy:

Don't know about anyone else, but I need another clue! Daz
 
a Bulgar is from Bulgaria, so a Meggar must me from Meggaria. think it's down in Dover.
 
UPDATE!

So I went back with my Meggar and found the issue!

Tested between the 2 switch lives at the switch and found a short (not picked up on my multimeter)

Started lifting floorboards to trace the cables and found a screw had just caught both switch lves in each t&e where they went through the joist!

These floorboards were lifted a week or so after I carried out the inspection and test!

The switch lives arcing together must be the cause of the LEDs burning out.

Sorted out the damage cables, tested and everything working bang on!

Appreciate all the advice and input given by everyone :)
 
now that's a good result. i assume the cables were just notched into the joists with no mechanical protection. well done for perseverance, and thanks for letting us know the outcome. and welcome to the world of finding awkward faults. :sunny:
 
now that's a good result. i assume the cables were just notched into the joists with no mechanical protection. well done for perseverance, and thanks for letting us know the outcome. and welcome to the world of finding awkward faults. :sunny:

The cables were drilled through the joist (not low enough down though) but also the nails were pretty long.

It's always nice to have a fault and find it! :)
 