I have just completed an EICR. The incoming gas pipe has been hidden behind kitchen units. I have dismantled the plinths, emptied the cupboards and used my inspection camera all to no avail. I cannot see any main bonding.

I can just get my hand through an inspection hole cut in the back of one unit and reach the incoming gas to get a crocodile clip on to it. I get a reading of 0.05Ω using a wander lead back to the MET.

In the CU there is a 10mm bonding cable which I have identified for the water, then there are 2 unidentified 6mm earthing/bonding conductors.

I have to admit I'm at a bit of a loss as to which code to give this? No main bonding is a C2, but with a reading of 0.05Ω!!?? The CU is approx 8m away from incoming gas pipe.

Any suggestions? Running a new 10mm would mean taking up laminate and kitchen floor tiles or making lots of holes in the ceiling which seems a bit crazy given such a low continuity reading which leads me to think it is bonded somewhere behind the units.
 
The amount of work required to rectify is irrelevant.

Is the gas pipe an extraneous conductive part?
 
Just a thought HHD, is there an external meter box ? If so the gas bond might be in there, otherwise a boiler will often give automatic continuity between all connected copper pipework ?
 
It's almost guaranteed that the current reading is at least partially via the gas appliances.

Testing the gas service for being extraneous is in my opinion essential to resolving this.
Then if it is extraneous introducing the Unidentified bonds in to the test to establish if they connect to the pipework will help
 
An earth connection must be accesible for regular inspection and testing, your reading means nothing as 0.05 ohms is only relevant to the equapotential conductor not the parralel reading of the pipes back to met via appliances, c2 imo from the info in your post.
 
And on your inspection list of supply characteristics and earthing arrangements, 'connection /continuity verified'
 
An earth connection must be accesible for regular inspection and testing, your reading means nothing as 0.05 ohms is only relevant to the equapotential conductor not the parralel reading of the pipes back to met via appliances, c2 imo from the info in your post.

What is the potential danger that you have identified?

His reading is 0.05 including all of the parallel paths so how can you say that they are not relevant?
 
I think I may have found a solution. The water bonding runs very close by and actually goes past the incoming gas, there is a fair bit of excess from the 10mm conductor, so I could divert it to the gas on its way to the incoming water pipe (keeping it continuous). I would have to make the inspection hole a fair bit bigger, but a small price to pay compared to taking up laminate.

What would you code this Dave? From your initial posts it seems as though you would class it as work that needs carrying out, yet your last post 'hints' towards this not being the case.


What is the potential danger that you have identified?

His reading is 0.05 including all of the parallel paths so how can you say that they are not relevant?
 
Last edited:
One other minor comment, can't see mention of the type of earth sys; if it's TNC-S then those 6mm should be min 10mm if indeed they are main bonding conductors.
 
I think I may have found a solution. The water bonding runs very close by and actually goes past the incoming gas, there is a fair bit of excess from the 10mm conductor, so I could divert it to the gas on its way to the incoming water pipe. I would have to make the inspection hole a fair bit bigger, but a small price to pay compared to taking up laminate.

What would you code this Dave? From your initial posts it seems as though you would class it as work that needs carrying out, yet your last post 'hints' towards this not being the case.

You haven't told us what the result of testing the gas pipe for being an extraneous part is yet, without that information I can't make a decision on coding it.

It is very hard to know exactly what I'd do without actually seeing the installation and being able to see all of the little pointers that allow you to decipher the story of how it got to being what it is now.
I'd be looking at the 6mm bonds to see if they look like they could be the original gas and water bonds with the 10mm being a later addition, and if 6mm is right for the age of the original installation.

Also I'd be looking at the water main and gas supply pipe to assist with dating the installation, and also look at whether it's a metallic or PE gas service pipe.
 
I have not tested to see if extraneous. I admit I have completely assumed it must be extraneous as its a metal pipe entering the house form a semi buried meter which has a metal supply pipe going into the ground. In addition how would you test to see if extraneous given the following.. Its tncs so even if I disconnected main earth to test would It not still be connected to other property's pipework? Also, in order to test to see if extraneous would I not have to find out out if the gas pipework is connected to any other extraneous parts (water etc) and disconnect from those?
 
Last edited:
I have not tested to see if extraneous. I admit I have completely assumed it must be extraneous as its a metal pipe entering the house form a semi buried meter which has a metal supply pipe going into the ground. In addition how would you test to see if extraneous? Its tncs so even if I disconnected main earth to test would It not still be connected to other property's pipework?
exactly,i would do what you said in post 8
 
I have not tested to see if extraneous. I admit I have completely assumed it must be extraneous as its a metal pipe entering the house form a semi buried meter which has a metal supply pipe going into the ground. In addition how would you test to see if extraneous given the following.. Its tncs so even if I disconnected main earth to test would It not still be connected to other property's pipework? Also, in order to test to see if extraneous would I not have to find out out if the gas pipework is connected to any other extraneous parts (water etc) and disconnect from those?

Ok, I don't think I've ever encountered a metal service pipe feeding a semi buried meter, only the yellow plastic with the metal Union/termination on at the joint to the anaconda.
Once upon a time it was a lot easier to work out as the gas board fitted a label specifically telling you that a plastic service pipe was installed.

Yes it is tricky in a TNCS supply, but the test will still give you a result which can help your decision making process. You may get a reading which shows negligible resistance to the TNCS Earth terminal, which as you have said, would indicate that the pipe is continuous metal to other properties. This in itself would confirm a requirement for bonding.

Your point about the gas pipe being connected electrically to the water pipework, usually via the boiler, is a very good one and it is something that I've discussed at great length with a few people.
I also have a concern on the interpretation of the regulation concerning the identification of extraneous parts which i still can't quite settle in my mind.

Is this a 70s/80s property by any chance? If it is then 6mm main bonds would be right for that era and would make me lean towards the two 6mm earths being the original main bonds.

Based on all of the information you've given so far I would make an observation that bonding conductors are present at the MET and testing indicates that the gas pipework has a low resistance connection to the MET but the location of the bonding connection to the pipe is not readily identifiable, also the bonding conductor identified at the MET is undersized according to the current standard. I would give this a C3 with the recommended improvement for safety being the connection of a 10mm bond at an accessible location.
 
Based on all of the information you've given so far I would make an observation that bonding conductors are present at the MET and testing indicates that the gas pipework has a low resistance connection to the MET but the location of the bonding connection to the pipe is not readily identifiable, also the bonding conductor identified at the MET is undersized according to the current standard. I would give this a C3 with the recommended improvement for safety being the connection of a 10mm bond at an accessible location.

Thanks Dave, very helpful reply - even though it's not my thread. So if I may take this slightly off topic, if you encountered a situation where you were extending a ring or a lighting circuit, and first go to check the main bonding - it exists in the CCU but you can't find where it terminates at the gas side. So you disconnect the gas bonding from the MET and continuity test it with the pipes at the meter - you get 0.05ohms, so surely the pipe is bonded. However, do you carry out the minor works on that install and treat this reading as a good enough indicator that it's bonded, or because it's not available for inspection at the gas pipe do you class it as not good enough and needs new bonding running first?

Thanks,
 
I think you will have a hard time proving whether the gas is extraneous or not .

Disconnect the 6mm bonding conductors from the MET and wander lead test them to the pipework , this will hopefully prove they are connected . C3 for inaccessible connections (Bloody kitchen fitters!)
 
I must say in the relatively short time (2-3 years) I have been undertaking electrical work I am surprised at the amount of times I have come across main bonding which has either been completely removed or made inaccessible. I can't work out if this is due to a lack of understanding on the part of the builder/plumber/kitchen fitter or that they don't care. Either way its a bit worrying!

The builder I work with is a very experienced builder, his standard of work is high and I have known him long enough to know he is honest. However, he had disconnected the main bonding on a recent job and was under the impression that it could just be removed nowadays if there was an RCD.:eek:
 
I must say in the relatively short time (2-3 years) I have been undertaking electrical work I am surprised at the amount of times I have come across main bonding which has either been completely removed or made inaccessible. I can't work out if this is due to a lack of understanding on the part of the builder/plumber/kitchen fitter or that they don't care. Either way its a bit worrying!

The builder I work with is a very experienced builder, his standard of work is high and I have known him long enough to know he is honest. However, he had disconnected the main bonding on a recent job and was under the impression that it could just be removed nowadays if there was an RCD.:eek:

Most of that is listening to the 'crack' in the wholesalers .
It's gospel of course.
 
I come across pipes not bonded all the time. Plumbers and builders seem to take great pleasure in cutting away our earth wires. It's a never ending battle with me trying to explain to a customer I have to bond their main incomers while they tell me it's been fine for the 30 years they have stayed in the property.
Every week I come across. It almost makes a mockery of why we have to do it when you consider how many properties don't have it, or have lost it .
 
It's always the plumbers who get their knickers in a twist about the gas pipe being bonded in the meter box, yet they will go looking for every single other bonding clamp to cut it off of the pipes.


Sent from my iPad using Tapatalk
 
It's always the plumbers who get their knickers in a twist about the gas pipe being bonded in the meter box, yet they will go looking for every single other bonding clamp to cut it off of the pipes.


Sent from my iPad using Tapatalk
Talking about plumbers cutting things off I went to a job the other day where the plumber cut the wiring centre out as he said it was in the way for his pipe work...he made sure he cut them as close as possible to the floor though as well. Other side of cupboard had a clear wall that he could of run up but that would of been too easy. I walked in see what he had done so I asked if he had been smoking crack....rang his boss who I was doing the job for and explained the simple connection of the new boiler and unvented upgrade had now turned into basically a full S-plan and would be costing £--- more now due to his muppet plumber. He wasn't happy to say the least.
 
Last edited by a moderator:
Without reference to any particular post, if a particular piece of pipe work is revealed not to be extraneous it therefore does not fulfill the requirements to be bonded by reg 411.3.1.1.

However, reg 528.3.4 would then need to be considered, for example if the internal pipe work is metal, then that would need to be bonded or effectively connected to the protective equipotential bonding.

Or have I interpreted that incorrectly.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
No main bonding seen but good continuity.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Midwest,
Replies
22
Views
17,664

Advert

Back
Top