Hi Sparkys!
one to scratch your head with: randomly one switch light trip the rcd sockets on the board?
have a look at the pic if it helps..
thank you
Fab
I am not certain what your question is, presumably you are asking why on certain occasions switching on a light switch can trip the RCD that is protecting the other half of the board.
I would say the most logical answer is that there is a neutral earth fault on one of the socket circuits and if there is enough load on the lighting then the redirected current can trip the sockets RCD.
morning Richard,
Thanks for your prompt response.
I apologise for my poor grammar, and yes that was the question. It only happen with this light switch, and not every time?
As it happen the other part of the board is only for the sockets, thats why I wrote the sockets RCD.
So you say its more a sockets problem than the lights??
The circuit that has a fault will trip it's own RCD, there cannot be a normal fault on the lighting circuit that can trip an RCD that is not connected to that circuit. However if the light in question was connected to the socket circuit then it would be possible.
Therefore the faulty circuit is one of the socket circuits, (Unless that light is part of a socket circuit).
Because the fault does not occur all the time it must be due to a change in the current drawn.
For the light to cause the RCD, that it is not connected to, to trip there must be a current flowing from the neutral bar back through one of the socket circuits.
Though it might be worth testing the RCD to ensure it is working correctly.
Might be along shot but if the live comes from the isolator to the two 6A MCB's first then it's extended to supply the RCD then a poor termination could maybe cause enough imbalance in the RCD to trip it, especially if there's arcing. Check all CU terminations and check for any busbars that are on the wrong side of a clamp.
Thanks again Richard,
looks like I have to get a professional in! I just bought that house and didn't really want to spend money on rewiring the full house!!
when I check the CU, whoever installed it put 3 differents MCB on the sockets side-hager- I had to buy 3 wylex ones! So better check the rest of it...the worst bit its that this house used to be rented and should have follow regulations??
cheers
cheers
If it's a Hager board why did you buy Wylex?
if you look at the pic you can see its a wylex board....thanks anyway
oops. Didn't notice that!
Back to the original question - I suspect you have a fault on the lighting circuit and a combination of "leakage" on the RCD side of the board - so when the lights are switched on it pushes the leakage over the trip level for the RCD.
You need a spark with a MFT and a earth leakage clamp meter so check this out
No worries lol!
yes I will get one, I thought there was something to do with the actual switch, something easy to sort out!
cheers, have a good week end!