If you have a ring final circuit then the recommendation is that the number of unfused spurs does not exceed the number of point on the ring. e.g. with ten sockets of the ring a maximum of 10 unfused spurs is recommended. The number of fused spurs is unlimited.

I'm clearly missing something here, as both you and Pete999 have mentioned this. I can't find anything in the current edition of the regs about a limit on number of spurs, although maybe I've read it in a previous edition.
 
I'm clearly missing something here, as both you and Pete999 have mentioned this. I can't find anything in the current edition of the regs about a limit on number of spurs, although maybe I've read it in a previous edition.
Have you looked at Appendix 15 in the BYB
 
I'm clearly missing something here, as both you and Pete999 have mentioned this. I can't find anything in the current edition of the regs about a limit on number of spurs, although maybe I've read it in a previous edition.
As I say it is a recommendation not a regulation.
It is mentioned in the OSG under standard circuits.
 
Having re-read the OP, I'm not sure we're talking about a ring....

"what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way"

I think he's talking radial.
 
Having re-read the OP, I'm not sure we're talking about a ring....

"what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way"

I think he's talking radial.

Interesting you could well be right. With main I assumed ring main.
If it is a radial then spurs are not possible, only branches, which are also unlimited though again recommended to be minimised (I think).
A 20A radial could be run all over the place without overloading a 2.5/1.5 mm² cable, though a large house circuit may experience nuisance tripping.
 
Appendix 15 is two pages. One on rings and one on radials. There's no reference to number of spurs off a ring.
You are correct it doesn't, but the OSG is what it is a guide BS7671 is a regulation and imo if someone is in doubt about something, the OSG is where to go and look.
 