Discuss spurs in the UK Electrical Forum area at ElectriciansForums.net
what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way , there will only be one large consumer a water heater .
you can take only 1 outlet as a spur from a ring final unless you fit a 13A FCU
1 spur per socket on the RFC See Appendix 15 BS 7671
what he said about what he above said ^^^^^. although 4mm is capable of handling the current in itself, adding several outlets to the same point on the rfc could overload the 2.5mm rfc cable especially if the point was close to one end of the rfc.
If you have a ring final circuit then the recommendation is that the number of unfused spurs does not exceed the number of point on the ring. e.g. with ten sockets of the ring a maximum of 10 unfused spurs is recommended. The number of fused spurs is unlimited.
An unfused spur will only supply a single point of use.
In practice you would be looking at the ring loading and ensuring that there were not a concentration of current drawn at one point of the ring.
I'm clearly missing something here, as both you and Pete999 have mentioned this. I can't find anything in the current edition of the regs about a limit on number of spurs, although maybe I've read it in a previous edition.
Have you looked at Appendix 15 in the BYB
Having re-read the OP, I'm not sure we're talking about a ring....
"what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way"
I think he's talking radial.
Interesting you could well be right. With main I assumed ring main.
If it is a radial then spurs are not possible, only branches, which are also unlimited though again recommended to be minimised (I think).
A 20A radial could be run all over the place without overloading a 2.5/1.5 mm² cable, though a large house circuit may experience nuisance tripping.
Appendix 15 is two pages. One on rings and one on radials. There's no reference to number of spurs off a ring.
You are correct it doesn't, but the OSG is what it is a guide BS7671 is a regulation and imo if someone is in doubt about something, the OSG is where to go and look.
OK, your choice.
It's a bit odd that the OSG adds a requirement that isn't present in the regs. My guess is that it's a hangover from the 15th edition and the writers of the OSG haven't noticed that the requirement has been removed from the regs.
OK, your choice.
So are you saying that as an example 10 sockets in a RFC you can't have 10 sockets as unfused spurs?
No. I'm saying you can have as many unfused spurs on a ring as you like, irrespective of the number of sockets on the ring. I believe that this complies with the current regs.
Yes Handy I can see where you are coming from now, well you live and learn
Reply to spurs in the UK Electrical Forum area at ElectriciansForums.net
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...