Widow(er) maker.....

Metal CU;
Brown & blue tails serving a shower sub-board (Don't know why they didn't use the spare ways on the rcd side!)
Flanders - don't worry, there is a mixed colour label on the cover, so all's good:eek:

Because it's an 80A RCD with 64A of OCPD connected to it already?
 
They did the 'bang test' and all was good so what could be wrong?!
Not happy looking at that - I'm getting some good standards in my training which pleases me, I even get a bit picky with the other mates I work alongside - well I don't want them to be producing sloppy work do I ?
 
Ok, you've won the watch
I just struggle to understand why anyone would do such an irresponsible thing.

I have come across this probably 10 times in the last year carrying out reports.

Effectively by having the cover off with that RCD still live you are breaching EAW Tegulations.
 
Breaching EAW would be the least of my worries! Switch off, carry out your safe isolation at the bottom of the main switch - all good; touch the lhs busbar, bang (and possibly dead).
This is a top post Polo !
A new step in the safe isolation procedure - check for sneaky supply that bypasses the isolator ...
 
Worse that the RCD not being on the load side of the isolator is the unprotected circuit leaving the CU on the brown and blue also in the top of the RCD.
 