I can't beleave there's no mix wiring colour label !!!! :D:D
 
  • Like
Reactions: DPG
I've seen that with two pairs of meter tails on a main switch before but never on the incoming side of an RCD :-O
 
Metal CU;
Brown & blue tails serving a shower sub-board (Don't know why they didn't use the spare ways on the rcd side!)
Flanders - don't worry, there is a mixed colour label on the cover, so all's good:eek:

Because it's an 80A RCD with 64A of OCPD connected to it already?
 
They did the 'bang test' and all was good so what could be wrong?!
Not happy looking at that - I'm getting some good standards in my training which pleases me, I even get a bit picky with the other mates I work alongside - well I don't want them to be producing sloppy work do I ?
 
Ok, you've won the watch
I just struggle to understand why anyone would do such an irresponsible thing.

I have come across this probably 10 times in the last year carrying out reports.

Effectively by having the cover off with that RCD still live you are breaching EAW Tegulations.
 
I have come across this probably 10 times in the last year carrying out reports.

Effectively by having the cover off with that RCD still live you are breaching EAW Tegulations.

Breaching EAW would be the least of my worries! Switch off, carry out your safe isolation at the bottom of the main switch - all good; touch the lhs busbar, bang (and possibly dead).
 
Breaching EAW would be the least of my worries! Switch off, carry out your safe isolation at the bottom of the main switch - all good; touch the lhs busbar, bang (and possibly dead).
This is a top post Polo !
A new step in the safe isolation procedure - check for sneaky supply that bypasses the isolator ...
 
  • Like
Reactions: hightower
Worse that the RCD not being on the load side of the isolator is the unprotected circuit leaving the CU on the brown and blue also in the top of the RCD.
 
  • Like
Reactions: DPG and Wilko
I have seen a similar house where the tails came from a main isolator (from a 100A fuse) in 10mm² to the first board, the second board was tapped off the incoming terminals of the first board and the third board was tapped off the incoming terminals of the second boards RCD!¬
 
Ps, it's a 100mA RCCB, yes that's 2 rings in one protective device, yes a 2.5 radial is doubled up in a protective device with a ring, and if anyone knows what type of 3871s they are then that would be fantastic as they were not written on.

Edit, Oh and the 6mm brown is feeding a shower!
 
  • Like
Reactions: Wilko
Ps, it's a 100mA RCCB, yes that's 2 rings in one protective device, yes a 2.5 radial is doubled up in a protective device with a ring, and if anyone knows what type of 3871s they are then that would be fantastic as they were not written on.

Edit, Oh and the 6mm brown is feeding a shower!

Another MK (Sentry?) board. Any chance they were built like this....surely not?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

polo1

Arms
~
Joined
Location
Glasgow
Business Name
GW Electrical & Security

Thread Information

Title
Widow(er) maker.....
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
polo1,
Last reply from
polo1,
Replies
22
Views
3,273

Advert