@Lister1987 I'm not really disagreeing, a couple of comments:

Even on an EICR doing IR tests as late as possible with everything back together is good practise, so if I've put an accessory screw through a conductor at a light switch or socket or caught something in a metal trunking cover it's picked up by the test. It's very embarrassing if a stupid mistake while carrying out T&I actually makes something worse!

Tracking down faults requires skills and thinking processes that are simply not taught as far as I can tell..
A real life EICR example from this year....IR testing an older CU with an RCD main switch.
Circuit 1, L+N bar to cpc bar is 80 Mohm (pass)
Circuit 2, L+N bar to cpc bar is 40 Mohms (pass)
Circuits 3-7, L+N bar to cpc bar is 0 Mohms.
Circuit 1 again, L+N bar to cpc bar is now 0 ohms.
Circuit 2 again, L+N bar to cpc bar is now 0 ohms.
Does anything you learn at college help you know what to do next? At this point no circuit can be turned on without tripping the RCD, and the tenant is getting cold. I'm sure a lot of the members on here would know exactly what to do next but would an average newly-qualified person who has just passed 2391-52?

Agreed.
Out of curiosty what was the issue in the end? My gut reaction is faulty coil in the RCD? :)
 
Out of curiosty what was the issue in the end? My gut reaction is faulty coil in the RCD? :)
Circuit 3 identified as the problem by removing all Neutrals and testing each circuit L+N to Earth on it's own.
Circuit 3 fed sub main to shed and utility room sockets. Splitting circuit traced the problem (to my surprise) to utility room.
Unplugging appliances one and a time revealed a faulty freezer gave up the ghost and was creating a dead short N to E.
 
Circuit 3 identified as the problem by removing all Neutrals and testing each circuit L+N to Earth on it's own.
Circuit 3 fed sub main to shed and utility room sockets. Splitting circuit traced the problem (to my surprise) to utility room.
Unplugging appliances one and a time revealed a faulty freezer gave up the ghost and was creating a dead short N to E.

We’re any of the MCBs tripping? I don’t get how circuit 1 and 2 passed and 3 + failed and then 1 and 2 then failed once IR tested again. Unless it wasn’t a true copper to copper N-E short and instead the insulation was breaking down and inducing voltage to E whilst testing?

Curious as to how those circuits were originally clear of fault :)
 
Last edited:
Before I started everything was apparently ok, nothing tripping, whether MCB's or the single main switch RCD.
When I IR tested circuit 3 at 500v it seems that I changed a dying appliance to a dead appliance (low resistance test afterwards showed < 1 ohm) so the freezer was a dead short between N and E as long as it was plugged in. As it was a single RCD board all the N's are joined, so when testing any circuit L+N to earth the same result (0) would then come back. Hence 1 and 2 passed until the freezer kicked the bucket, then after the freezer snuffed it the whole N bar to CPC bar had a dead short.
 
Yeah that was my line of thoughts as well thanks so much for clarifying all these extra bits of knowledge and experiences sure help! Double pole RCBOs would certainly help narrow down global faults like that eh?

Did you buy her a new fridge after killing it off haha 🤣
 

Reply to I thought short courses were fine. Just done a week on site. Now i think they're not fit for purpose. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Does anyone else get emails and phone calls from companies and agencies say we seen your CV and we want you to apply for our job. And when you...
Replies
4
Views
559
I'm unsure if I should be an electrician or maybe another trade is better. I have basically completed my first year of a foundation in...
Replies
9
Views
668
Maybe I've just been lucky, but I very rarely have an issue with customers paying, the vast majority have paid straight away or within a few days...
Replies
33
Views
2K
I recently sold my Renault Trafic as it had done 214,000 miles and I also wanted something more economical. I bought the Citroen Berlingo LWB. A...
Replies
34
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
578

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock