Non-flame propagating would be term;

Non-flame propagating. Liable to ignite as a result of an applied flame but, after the flame is removed, does not propagate further and extinguishes itself within a limited time.

That term however applies to containment systems.

The Regulation pertaining to domestic CUs is;

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation
132.12.
NOTE: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.


I don't normally berate other members but I'm sorry, get a clue. Wiring Regulations are non-statutory (not law), the statue (law) applicable to Electricians and Electrical Installations is Electricity at Work 1989.
If you're going to spout shite,please make it informed and researched shite, other you just look stupid.
Your forgetting the EICRs for rented properties are now a legal requirement. And the guidance to landlords is that the EICR ensures there properties Comply with the latest version of BS7671. An EICR was not a mandatory document. But has that changed. I will not comment yes or no because I am not a trained lawyer barrister or judge. Thats the whole point. We are only putting our personal view points on a forum. A court and there interpretation of case law is another matter entirely
 

Soi disant

Esteemed
Reaction score
226
Yes, but when you read the 18th you see that it does not contain a single standard which existing installations have to meet - it only applies to the design, erection, additions, alterations, and verification of electrical installations designed after 31st December 2018.

The guidance you quote doesn't change what the numpty lawyers wrote. If they even were lawyers, and not junior off-shore office clerks working self-employed for Serco.
 

Soi disant

Esteemed
Reaction score
226
Your forgetting the EICRs for rented properties are now a legal requirement.
They aren't, strictly speaking - there's nothing in the law which makes them so. It's just that it's the way that makes the most sense. It's a bit like Part P not actually requiring work to comply with BS 7671, but the reality being it makes precious little sense to do otherwise.


And the guidance to landlords is that the EICR ensures there properties Comply with the latest version of BS7671.
Except of course that is impossible, unless you use the special definition of "comply".

A court and there interpretation of case law is another matter entirely
Which in all probability will never happen - any landlord faced with a report he doesn't like could have the place totally rewired using russ andrews cryogenically treated cables and a gold-plated CU for less than the cost of lawyers.
 
Reaction score
148
Yes, but when you read the 18th you see that it does not contain a single standard which existing installations have to meet - it only applies to the design, erection, additions, alterations, and verification of electrical installations designed after 31st December 2018.

The guidance you quote doesn't change what the numpty lawyers wrote. If they even were lawyers, and not junior off-shore office clerks working self-employed for Serco.
It doesn't matter what the 18th says as it has no legal standing. The legal authority comes from the landlords having a legal obligation to have an eicr that complies with the 18th. And thats from government legislation not any edition of BS7671.
 

Soi disant

Esteemed
Reaction score
226
It doesn't matter what the 18th says as it has no legal standing. The legal authority comes from the landlords having a legal obligation to have an eicr that complies with the 18th. And thats from government legislation not any edition of BS7671.
Since you clearly disagree with
They aren't, strictly speaking - there's nothing in the law which makes them so.
perhaps you'd like to quote the part of The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - http://www.legislation.gov.uk/uksi/2020/312/contents/made which imposes a legal obligation to have an eicr that complies with the 18th.
 
Reaction score
148
Since you clearly disagree with

perhaps you'd like to quote the part of The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - http://www.legislation.gov.uk/uksi/2020/312/contents/made which imposes a legal obligation to have an eicr that complies with the 18th.
And thats exactly where this thread gets a definitive answer phew 😅 There is a lot of information out there. But nothing in government guidelines that says Landlords EICRs or anyone else's EICRs have to legally comply with the current edition of the regulations. Just a legal requirement for landlords to have an EICR carried out every 5 years. 👍
 

Lister1987

-
Trainee
Esteemed
Reaction score
827
And thats exactly where this thread gets a definitive answer phew 😅 There is a lot of information out there. But nothing in government guidelines that says Landlords EICRs or anyone else's EICRs have to legally comply with the current edition of the regulations. Just a legal requirement for landlords to have an EICR carried out every 5 years. 👍
Given that the wording in the above legislation doesn't, iirc, state that the outcome MUST be satisfactory, a LL could just have an EICR undertaken to 18th edition, have it come back as unsatisfactory and yet still have met the requirements of the legislation. Surely not?
 

loz2754

-
Esteemed
Arms
Reaction score
1,347
Given that the wording in the above legislation doesn't, iirc, state that the outcome MUST be satisfactory, a LL could just have an EICR undertaken to 18th edition, have it come back as unsatisfactory and yet still have met the requirements of the legislation. Surely not?
Indeed.
But the law further stipulates that any remedial work that is deemed necessary, resulting in the unsatisfactory report, must be done within 28 days from when the report was issued.
 

Pretty Mouth

-
Esteemed
Arms
Reaction score
796

The backs of boards should be sealed on reading this, and manufactures can bring new.materials to market if they prove non combustable.
Care homes and the.like ain't part of this even tho no differnece in my eyes ..

And over all they are blaming bad workmanship, but the work could of been good for 10 years prior to fire.
The IET also put out other guidance in a Q+A, apparently contradicting the guidance you linked to above. The forum censors links to wiring matters, but if you put "Consumer units: a brief overview" into your search engine (quote marks included) it should come up top of the list:


When I put cables into a new metal consumer unit, do I have to use intumescent glands to enforce the fire protection of the consumer unit?

No, the metal consumer unit is designed to encase a fire within it and restrict the likelihood that a fire may spread. Manufactures’ have carried out exhaustive tests on this issue and have found that the cable entry does not have to continue the fire rating of the consumer unit, for it to be effective. The only requirement is to keep IPXXD or IP4X on the horizontal surfaces (Reg 416.2.1) and IPXXB or IP2X on all other surfaces (Reg 416.2.2). Intumescent glands and sealants may be used to ensure the IP ratings are maintained, but they are not a requirement and existing methods of ensuring IP are acceptable.
 

SparkySy

-
Esteemed
Arms
Reaction score
529
Very interesting analysis of this ver hot topic! Above this is why it is down to the inspectors own engineering judgement on the day to an extent. As there are no real rules or legislation to cover every eventually we may come across. The electrical industry is so varied and wide that a dossier to cover all would be ridiculous in size!
 

telectrix

-
Mentor
Esteemed
Arms
Reaction score
62,316
Very interesting analysis of this ver hot topic! Above this is why it is down to the inspectors own engineering judgement on the day to an extent. As there are no real rules or legislation to cover every eventually we may come across. The electrical industry is so varied and wide that a dossier to cover all would be ridiculous in size!
almost as bigb as my dossier at Police HQ., Anfield.
 