I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back.

Our company just had its EICR done. The tester gave us a C2 for a number of DB’s which don’t have Surge Protection Device installed, these DBs with the C2 do have lighting and emergency lighting circuits.
Do we have to have these SPD’s installed now because of 18th edition amendment 2 or should it be a C3 for a recommended device in the DB’s for old boards.

Many thanks.
 
I think you need to find a different company to test your installation
C2 is way over the top for lack of spd in my opinion.
 
C1 – There is a danger present, risk of injury and immediate remedial action required.
C2 – There is a potential danger present and urgent remedial work is required.
C3 – Improvement is recommended.

how can anyone justify a surge protection issue as a potential danger?
 
  • Like
Reactions: DPG and nicebutdim
I presume that the reasoning is that there are life safety systems present (i.e. the emergency lighting installations). That said I would probably personally consider the classification of the Observation to be rather harsh.
 
  • Like
Reactions: nicebutdim
C1 – There is a danger present, risk of injury and immediate remedial action required.
C2 – There is a potential danger present and urgent remedial work is required.
C3 – Improvement is recommended.

how can anyone justify a surge protection issue as a potential danger?
Exactly, having no SPD isn't a potential danger with urgent remedial work required.
 
I presume that the reasoning is that there are life safety systems present (i.e. the emergency lighting installations). That said I would probably personally consider the classification of the Observation to be rather harsh.
I agree, its defiantly harsh to put it as a C3
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
sheffield

Thread Information

Title
Surge Protection Device on old installations
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
punkin,
Last reply from
punkin,
Replies
7
Views
1,376

Advert