Too much worry not enough wiring, pull your skirts up...
 
Does the legislation say "Metal" or "Flame proof" or even "Flame retardant"? Haven't got my copy to hand.
Non-Combustible is the phrase I believe - and an example is given of steel. No idea if the BS standard for CUs says something different now, but there's no reason in principle why they couldn't find a suitable plastic or other material that was non-combustible - I just suspect it would cost more so they went with the cheapest option.

It would be handy to have a non-combustible AND non-conducting material for TT installations.
 
Fibreglass is non-combustable and non-conducting, but would be expensive to manufacture compared to moulding plastic and stamping out a metal CU.
 
https://electrical.----------/wirin...ble-enclosure-requirement-for-consumer-units/

The backs of boards should be sealed on reading this, and manufactures can bring new.materials to market if they prove non combustable.
Care homes and the.like ain't part of this even tho no differnece in my eyes ..

And over all they are blaming bad workmanship, but the work could of been good for 10 years prior to fire.
 
You may be over-thinking it. That bit in the Introduction says that non-compliant installations do not have to be upgraded. It does not say that existing installations that have been installed in accordance with earlier editions of the regulations are deemed to comply with this edition if they are not unsafe for continued use.

What has yet to be determined by a court ruling is whether the law requiring that "electrical safety standards are met" means that an existing installation has to comply with every aspect of BS 7671:2018 or only some, and if the latter, which.

A consensus seems to have emerged that it must have no non-compliances coded as C1 or C2. Superficially reasonable, if we think it reasonable to enshrine in law the can of worms which is the significantly indeterminate nature of many C2-or-C3 decisions ¹ .

But, and this is where you may be under-thinking it, there is no basis in fact for any determination based on C1/C2/C3. None whatsoever.

The lawmakers have done a truly abysmal job. Leaving aside the is-it-a-C2-or-a-C3 issue, they could have required landlords to have an EICR carried out which complied with the current edition of the Wiring Regulations (i.e. the carrying out of the EICR had to be in accordance, not the installation) and that any C1 or C2 conditions be rectified within x days and a new EICR done.

But they didn't. What they did was unbelievable, really. (Or is it, sadly, all too believable?)

They required that private landlords must ensure that the electrical safety standards are met during any period when the residential premises are occupied under a specified tenancy.

And they defined "electrical safety standards" as "the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018".
QUOTE]

From the Gov guidance document @timhoward linked to above, section 8:
 
Non-Combustible is the phrase I believe - and an example is given of steel. No idea if the BS standard for CUs says something different now, but there's no reason in principle why they couldn't find a suitable plastic or other material that was non-combustible - I just suspect it would cost more so they went with the cheapest option.

It would be handy to have a non-combustible AND non-conducting material for TT installations.
Non-flame propagating would be term;

Non-flame propagating. Liable to ignite as a result of an applied flame but, after the flame is removed, does not propagate further and extinguishes itself within a limited time.

That term however applies to containment systems.

The Regulation pertaining to domestic CUs is;

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation
132.12.
NOTE: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.

How about because the Wiring Regulations, and hence the law, do not mandate it?

Or because the fact that at the time you did the inspection plastic CUs could still be installed in offices, shops, schools, pubs, restaurants, care homes, indicated to you that plastic CUs did not need to be replaced as a matter of urgency?
I don't normally berate other members but I'm sorry, get a clue. Wiring Regulations are non-statutory (not law), the statue (law) applicable to Electricians and Electrical Installations is Electricity at Work 1989.
If you're going to spout rubbish,please make it informed and researched rubbish, other you just look stupid.
 
  • Creative
Reactions: Mike Johnson
Non-flame propagating would be term;

Non-flame propagating. Liable to ignite as a result of an applied flame but, after the flame is removed, does not propagate further and extinguishes itself within a limited time.

That term however applies to containment systems.

The Regulation pertaining to domestic CUs is;

421.1.201 Within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall:
(i) have their enclosure manufactured from non-combustible material, or
(ii) be enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation
132.12.
NOTE: Ferrous metal, e.g. steel, is deemed to be an example of a non-combustible material.


I don't normally berate other members but I'm sorry, get a clue. Wiring Regulations are non-statutory (not law), the statue (law) applicable to Electricians and Electrical Installations is Electricity at Work 1989.
If you're going to spout rubbish,please make it informed and researched rubbish, other you just look stupid.
Your forgetting the EICRs for rented properties are now a legal requirement. And the guidance to landlords is that the EICR ensures there properties Comply with the latest version of BS7671. An EICR was not a mandatory document. But has that changed. I will not comment yes or no because I am not a trained lawyer barrister or judge. Thats the whole point. We are only putting our personal view points on a forum. A court and there interpretation of case law is another matter entirely
 
Yes, but when you read the 18th you see that it does not contain a single standard which existing installations have to meet - it only applies to the design, erection, additions, alterations, and verification of electrical installations designed after 31st December 2018.

The guidance you quote doesn't change what the numpty lawyers wrote. If they even were lawyers, and not junior off-shore office clerks working self-employed for Serco.
 
  • Like
Reactions: David Anthony
Your forgetting the EICRs for rented properties are now a legal requirement.
They aren't, strictly speaking - there's nothing in the law which makes them so. It's just that it's the way that makes the most sense. It's a bit like Part P not actually requiring work to comply with BS 7671, but the reality being it makes precious little sense to do otherwise.


And the guidance to landlords is that the EICR ensures there properties Comply with the latest version of BS7671.
Except of course that is impossible, unless you use the special definition of "comply".

A court and there interpretation of case law is another matter entirely
Which in all probability will never happen - any landlord faced with a report he doesn't like could have the place totally rewired using russ andrews cryogenically treated cables and a gold-plated CU for less than the cost of lawyers.
 
  • Like
Reactions: Dartlec
Yes, but when you read the 18th you see that it does not contain a single standard which existing installations have to meet - it only applies to the design, erection, additions, alterations, and verification of electrical installations designed after 31st December 2018.

The guidance you quote doesn't change what the numpty lawyers wrote. If they even were lawyers, and not junior off-shore office clerks working self-employed for Serco.
It doesn't matter what the 18th says as it has no legal standing. The legal authority comes from the landlords having a legal obligation to have an eicr that complies with the 18th. And thats from government legislation not any edition of BS7671.
 
It doesn't matter what the 18th says as it has no legal standing. The legal authority comes from the landlords having a legal obligation to have an eicr that complies with the 18th. And thats from government legislation not any edition of BS7671.
Since you clearly disagree with
They aren't, strictly speaking - there's nothing in the law which makes them so.
perhaps you'd like to quote the part of The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - http://www.legislation.gov.uk/uksi/2020/312/contents/made which imposes a legal obligation to have an eicr that complies with the 18th.
 
Since you clearly disagree with

perhaps you'd like to quote the part of The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020 - http://www.legislation.gov.uk/uksi/2020/312/contents/made which imposes a legal obligation to have an eicr that complies with the 18th.
And thats exactly where this thread gets a definitive answer phew ? There is a lot of information out there. But nothing in government guidelines that says Landlords EICRs or anyone else's EICRs have to legally comply with the current edition of the regulations. Just a legal requirement for landlords to have an EICR carried out every 5 years. ?
 
And thats exactly where this thread gets a definitive answer phew ? There is a lot of information out there. But nothing in government guidelines that says Landlords EICRs or anyone else's EICRs have to legally comply with the current edition of the regulations. Just a legal requirement for landlords to have an EICR carried out every 5 years. ?
Given that the wording in the above legislation doesn't, iirc, state that the outcome MUST be satisfactory, a LL could just have an EICR undertaken to 18th edition, have it come back as unsatisfactory and yet still have met the requirements of the legislation. Surely not?
 
Given that the wording in the above legislation doesn't, iirc, state that the outcome MUST be satisfactory, a LL could just have an EICR undertaken to 18th edition, have it come back as unsatisfactory and yet still have met the requirements of the legislation. Surely not?
Indeed.
But the law further stipulates that any remedial work that is deemed necessary, resulting in the unsatisfactory report, must be done within 28 days from when the report was issued.
 
  • Agree
Reactions: old man sparky

The backs of boards should be sealed on reading this, and manufactures can bring new.materials to market if they prove non combustable.
Care homes and the.like ain't part of this even tho no differnece in my eyes ..

And over all they are blaming bad workmanship, but the work could of been good for 10 years prior to fire.
The IET also put out other guidance in a Q+A, apparently contradicting the guidance you linked to above. The forum censors links to wiring matters, but if you put "Consumer units: a brief overview" into your search engine (quote marks included) it should come up top of the list:


When I put cables into a new metal consumer unit, do I have to use intumescent glands to enforce the fire protection of the consumer unit?

No, the metal consumer unit is designed to encase a fire within it and restrict the likelihood that a fire may spread. Manufactures’ have carried out exhaustive tests on this issue and have found that the cable entry does not have to continue the fire rating of the consumer unit, for it to be effective. The only requirement is to keep IPXXD or IP4X on the horizontal surfaces (Reg 416.2.1) and IPXXB or IP2X on all other surfaces (Reg 416.2.2). Intumescent glands and sealants may be used to ensure the IP ratings are maintained, but they are not a requirement and existing methods of ensuring IP are acceptable.
 
Very interesting analysis of this ver hot topic! Above this is why it is down to the inspectors own engineering judgement on the day to an extent. As there are no real rules or legislation to cover every eventually we may come across. The electrical industry is so varied and wide that a dossier to cover all would be ridiculous in size!
 
  • Like
Reactions: i=p/u
Very interesting analysis of this ver hot topic! Above this is why it is down to the inspectors own engineering judgement on the day to an extent. As there are no real rules or legislation to cover every eventually we may come across. The electrical industry is so varied and wide that a dossier to cover all would be ridiculous in size!
almost as bigb as my dossier at Police HQ., Anfield.
 
almost as bigb as my dossier at Police HQ., Anfield.
Can't be, last I heard some Scouse git nicked it.....thieving bastards will take anything these days!
 
  • Like
Reactions: LastManOnline
My inspector from Napit basically advised me of the same potential situation as the OP suggested
I was discussing with him EICR coding, whereas I am generally more lenient on my coding than some, he suggested 'why take the chance? It’s you who will end up in court trying to justify it against some hard nosed lawyer waving the code breakers book at you!’
And sadly, the way the world is heading I have to agree with him, trying to be honest and doing the right thing is just giving more leverage to a lawyer if god forbid it ever got that far
so from now on I have tightened my coding up and have been now using the code breakers book rather than the BPG no. 4 which I used to use as a reference
 
Posted April 1, 2013
"The Ferrari F1 team fired their entire pit crew yesterday."This announcement followed Ferrari's decision to take advantage of the British government's 'Work for your Dole' scheme and employ some Scouse youngsters.

The decision to hire them was brought about by a recent TV documentary on how unemployed youths from Toxteth, Liverpool were able to remove a set of wheels in less than 6 seconds without specialist equipment, whereas Ferrari's existing crew could only manage it in 8 seconds with millions of pounds worth of high tech gear.

It was thought to be an excellent, bold move by the Ferrari management team, as most races are won and lost in the pits, thus giving Ferrari a massive advantage over every other team.

The scouse lads were brilliant at their home practice sessions, however, Ferrari got more than they bargained for! At the crew's first real race practice session at Le Mans, not only was the scouse pit crew able to change all four wheels in under 6 seconds but, within 12 seconds, they had re-sprayed, re-badged and sold the car to the McLaren team for 8 cases of Stella, a bag of ganja and some photos of Lewis Hamilton's bird in the shower.
 
nothing in government guidelines that says Landlords EICRs or anyone else's EICRs have to legally comply with the current edition of the regulations.
“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(3);
From ESPRS definitions
 
Just to add the fun, had a call from a client today who had a report that says "satisfactory", despite having some C2s on it!

Agent is the one that picked up there were some C2s and is demanding that remedials be done, although the front page of the report says 'satisfactory'....

Lawyers would have fun with that one! - Waiting to see a copy before I decide in which way the inspector got it wrong....
 
The EICR for my current gaff has got a satisfactory EICR with a few C3s......and an FI, so in theory not satisfactory right? ?
 
I'll start a new thread I think - but seen the report now and an NICEIC Approved Contractor has issued a 'satisfactory' report with 8 C2s ?‍♂️

One of which is no RCD for fault protection on a PME system with adequate Zs on all circuits (according to his certificate...)

But apparently there is RCD protection for LV circuits in the bathroom (tick)? Possible there's a local 7288 I guess to give him partial benefit of the doubt...

When the quality of EICRs given out is as bad as most of the ones I've seen, then worrying about minor edge cases seem less of an issue! Though to be fair the ones that get seen by others are usually the ones where there is a question...

Mind you hes only quoted £350 for a Consumer Unit upgrade, which is less than me probably - probably making it back on the £80 he wanted to upgrade main earthing (though it is apparently 16mm) - and £45 to run main bonding to the gas meter which seems like it may be in the same cupboard....
 
Not too bad then, just 8 c2s
 
The EICR for my current gaff has got a satisfactory EICR with a few C3s......and an FI, so in theory not satisfactory right? ?
Maybe they got the information required between doing the test sheet and completing the front page? ?
 
My inspector from Napit basically advised me of the same potential situation as the OP suggested
I was discussing with him EICR coding, whereas I am generally more lenient on my coding than some, he suggested 'why take the chance? It’s you who will end up in court trying to justify it against some hard nosed lawyer waving the code breakers book at you!’
And sadly, the way the world is heading I have to agree with him, trying to be honest and doing the right thing is just giving more leverage to a lawyer if god forbid it ever got that far
so from now on I have tightened my coding up and have been now using the code breakers book rather than the BPG no. 4 which I used to use as a reference
If there was a clear concensus then there wouldn't be a difference between the two - that is part of the trouble.

There should be industry wide and standard guidance (clearly not to cover every situation, but in common scenarios) - with if necessary a stricter guidance for tenanted properties if that is the intention of the law

For example - that any property with cabling less than 50mm in the wall is always a C2 - or that all circuits in a rented properly must have RCD additional protection regardless...
 
  • Like
Reactions: timhoward
or that all circuits in a rented properly must have RCD additional protection regardless...

I had a great one for remedials recently.
C1 for lack of RCD protection
C1 for plastic CU.
C2 for lack of two colours sticker
C2 for lack of last inspection sticker ?!
C2 for lack of RCD test sticker
C2 for cables inadequately supported

Apparently a quote of £1200 for a new RCBO board and "other urgent safety-critical repairs" though I didn't see this for myself.

So I slapped 3 stickers on, including one the inspector should have put on himself, knocked in 3 cable clips, then looked at the RCD issue.
It was a split load board and 4 of the 5 circuits on the non-RCD side had RCBOs. So only one B6 in the whole board was not RCD protected and it's sole purpose in life was supplying the light in the cupboard where the CU and meter was. And that got a C1! Needless to say I didn't change the board.
 
Time will tell what code lack of AFDDs will be in 5 years time, only 99.99999% of properties affected by that one....some very unhappy landlords who were overcharged for a dual RCD board this time round no doubt...
 
  • Like
Reactions: DPG and timhoward
I had a great one for remedials recently.
C1 for lack of RCD protection
C1 for plastic CU.
C2 for lack of two colours sticker
C2 for lack of last inspection sticker ?!
C2 for lack of RCD test sticker
C2 for cables inadequately supported

Apparently a quote of £1200 for a new RCBO board and "other urgent safety-critical repairs" though I didn't see this for myself.

So I slapped 3 stickers on, including one the inspector should have put on himself, knocked in 3 cable clips, then looked at the RCD issue.
It was a split load board and 4 of the 5 circuits on the non-RCD side had RCBOs. So only one B6 in the whole board was not RCD protected and it's sole purpose in life was supplying the light in the cupboard where the CU and meter was. And that got a C1! Needless to say I didn't change the board.
Not even AFDDs should get to £1200 for a new board unless it's ludicrously large!
 
I had a great one for remedials recently.
C1 for lack of RCD protection
C1 for plastic CU.
C2 for lack of two colours sticker
C2 for lack of last inspection sticker ?!
C2 for lack of RCD test sticker
C2 for cables inadequately supported

Apparently a quote of £1200 for a new RCBO board and "other urgent safety-critical repairs" though I didn't see this for myself.

So I slapped 3 stickers on, including one the inspector should have put on himself, knocked in 3 cable clips, then looked at the RCD issue.
It was a split load board and 4 of the 5 circuits on the non-RCD side had RCBOs. So only one B6 in the whole board was not RCD protected and it's sole purpose in life was supplying the light in the cupboard where the CU and meter was. And that got a C1! Needless to say I didn't change the board.
The guy who did that should be :

a) ejected from his scheme
b) charged with fraud.
 
Maybe they got the information required between doing the test sheet and completing the front page? ?
They didn't even do that right, I'm on a TN-C apparently ?
 
  • Funny
Reactions: Dartlec
And sadly, the way the world is heading I have to agree with him, trying to be honest and doing the right thing is just giving more leverage to a lawyer if god forbid it ever got that far
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
 
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
What was it about the concrete that caused the damage mate?
 
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
Unfortunately price of insurance seems to be no guarantee that they'll be any good when you need them - and the only way to find out is to need them, which isn't ideal!

Besides which, trying to work out who is actually doing the underwriting is often not simple and turns out to be the same very few names in any case...

I guess at least you get someone saying you weren't negligent! Sounds like the builder's insurance should be stepping in, but no doubt they'll claim it's an 'electrical issue...' etc...
 
What was it about the concrete that caused the damage mate?
They put a retardent in it. Retardent was acidic. This was during the building boom in the noughties. Concrete was delivered on site hours before the brickies arrived due to demand. Issues resulting from the retardent now manifesting
 
I guess at least you get someone saying you weren't negligent! Sounds like the builder's insurance should be stepping in, but no doubt they'll claim it's an 'electrical issue...' etc...
Yes. Its a "cu de sac" basically. Builder long gone anyway. But when you consider the pages and pages of stuff you receive on paying for public liability it would be really nice if someone told you upfront what you can realistically expect to happen in the event of a claim. I am disappointed but can't say I, m totally surprised. Yes, it cost me a night or two, s sleep but I am determined to draw a, line in the sand and not allow it fester. I, m stung but not bankrupted. Am grateful for that
 
  • Like
Reactions: nicebutdim
Have being reading this thread with great interest. No need for me to elaborate on previous posts concerns about what we as sparks "are leaving ourselves open for" as we go about our normal daily work. I am currently going through my first professional liability claim. 25 years with same insurance company. Have deliberately gone with the "top of the range" provider (840.00 euros a year for a sole trader).
In the case I, m involved in the issue has to do with the type of concrete used by the builder which has caused damage to cabling. Here's the interesting bit. Because I personally have not being negligent in any aspect my work, the insurance company feel they have no liability. It has been suggested to me to pursue the concrete supplier.
Not the kind of service I expected, but as "welchyboy" alludes to, its the "way the world is"
You say it’s a claim on your prof. Indemnity ins was the matter over an eicr you carried out I take it, or with cabling that you personally installed?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bristol
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
C3s putting you in harms way ??
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
151

Thread Tags

Tags Tags
putting

Advert

Thread statistics

Created
old man sparky,
Last reply from
UNG,
Replies
151
Views
15,545

Advert