I have seen a similar house where the tails came from a main isolator (from a 100A fuse) in 10mm² to the first board, the second board was tapped off the incoming terminals of the first board and the third board was tapped off the incoming terminals of the second boards RCD!¬
Ps, it's a 100mA RCCB, yes that's 2 rings in one protective device, yes a 2.5 radial is doubled up in a protective device with a ring, and if anyone knows what type of 3871s they are then that would be fantastic as they were not written on.
Edit, Oh and the 6mm brown is feeding a shower!
Another MK (Sentry?) board. Any chance they were built like this....surely not?
I don't think so, in both cases the add on is the exact same type of cable as the supply cable, I do come across a fair few of these, all linked in the same cable as the supply.
Anyone here around when these were stocked who can shed any light? I C2ed mine on the EICR.
Breaching EAW would be the least of my worries! Switch off, carry out your safe isolation at the bottom of the main switch - all good; touch the lhs busbar, bang (and possibly dead).
that's what the proving unit is for