I am in the process of designing the electrical installation of a community centre, and have a question about the provision of three phase lighting for a large function room containing 18 36W LED fittings. All of the light fittings are to be switched simultaneously. Would it be possible to connect these lights in a three phase Delta configuration using 400V LED driver units, by connecting 6 light fittings/Drivers to each line, thereby ensuring a constant balanced load on each line? Presumably, I would not need to provide a neutral for each line, and could get away with just providing earthing for each fitting? Does anyone think that this design would be unsuitable?
 
Of course perfectly balanced single phase loads will function perfectly well without a neutral until something fails and then things don't function so well.
 
how can a single phase load function without a neutral, unless it's 415V s.p.
 
Ok because of the phase angle/voltage difference at each 120 degree angle but I can see that on say a single circuit like a water heater but separate circuits, that works? I can't quite think this out. Mmm maybe...why not indeed or even why
 
the singlephase load requires 240V. the only way to get that from a 3 phase 415V supply is Ph -N, N being the star point.
 