Thanks for your response. I have assessed it as far a I can and as you say cables are buried in plaster. The house is a dry house but obviously I can’t rule out that one day there could be a leak. I’ve changed all light fittings and switches to class 2, I’ve put a sticker on the board stating circuit number has no provision for earth and fittings must not be replaced with metal. I’ve put it in writing to landlord that in my opinion he should look at rewiring or installing cpc to that circuit and told him the safety aspects of circuits being earthed. I’ve done all paperwork and classed it as c3 improvement recommend. I don’t see there is much more I can do.The code that is applied is the decision of the inspector of the installation as they have the awareness to be able to assess the level of risk caused by the observation.
In the case of the failed conduit a fault from line to the conduit would result in the conduit becoming live, possibly over a large area of the installation.
In the case of a cable installed in an insulating medium this hazard does not arise and so the risk is negligible.
In the case of a normal domestic installation (if such a thing exists) cables are often buried in plaster that, if wet, could provide a potentially partially conductive path, however the likelihood of it being wet may be very low, and so on. All these aspects should be taken into account to adequately assess the level of risk, this can often be done with minimal assessment based on previous experience, occasionally things catch you out.
, when asking for help on the forum you will get various opinions be they to your liking or not, reading through the thread I see no issue with responses and even those you disagree with have apologised as to how you reacted to them, if you are on an active course then please apply for our trainee section where your questions will be answered with full respect of your trainee position, you deemed some questions a bit negative for your liking but with full respect they are questions which I would expect to be put your way, may I ask what qualifications you have and do you have any onsite trained experience like a full apprenticeship, this knowledge will allow members to respond appropriately and not to make assumptions and consequently pull the thread off course as you bounce off each other.