You'd have to see if the disconnection times could be met based on Ze, have you I.R tested every circuit L-E and N-E ?
 
You say it's been ok for 2 weeks, then the nuisance tripping has started. You also mention the cabinet with the 100mA RCD is external. Is this tripping happening at the same time of day/night? Have the atmospheric conditions changed? I'm wondering if the cause may be condensation related.
 
You say it's been ok for 2 weeks, then the nuisance tripping has started. You also mention the cabinet with the 100mA RCD is external. Is this tripping happening at the same time of day/night? Have the atmospheric conditions changed? I'm wondering if the cause may be condensation related.

It could be something as simple as this Tony
 
Re OP's #1: Which two final circuits?

You mention a TN&N board converted to SP. How many final circuits are there?

Suggestions:

Test the IR of electric ovens, hot wire element electric hobs, washing machines and tumble dryers and dishwashers, immersion heater.

Take a close look inside any outside light fittings and switches.

Pour 2-3 gallons of water around the earth electrode.

Check tightness and solidity of all connections.

Carefully remove sockets and look behind them for securing screws close to live conductors.
 
Hi - Agree Murdoch and Strima I would not change out 100mA S type without a test result showing it's at fault. As others have said, it's quite likely a N-E fault exists. If it's in a final circuit unfortunately the single pole rcbo won't remove it from play.
Some questions and thoughts -
What parts of this installation are new?
Any patterns to the tripping?
What is the site Ze? Locate the rod and confirm the impedance of connection from rod to MET and CU earth bar with wander lead. Repair if required.
How long is the underground SWA linking cabinet to CU? What protects this cable? What were the cable IR results please? Carefully check all connections from cutout to CU and the polarity.
Happy Hunting :)
 
You could ramp test the RCD first with everything off and then with everything on to get an idea of leakage current on the installation.
 
Suggestions:

Test the IR of electric ovens, hot wire element electric hobs, washing machines and tumble dryers and dishwashers, immersion heater.

Out of interest how do you test the element in the appliance? Do you have to dis-assemble?