Octopus
I’ve thought about trying a 300mA - there’s over 20 Rcbo’s
Wrong approach imho
Changing parts instead of investigating and testing is rarely a successful approach...
I’ve thought about trying a 300mA - there’s over 20 Rcbo’s
Until you confirm the cause of the tripping there's no point swapping parts out in a vain hope it might work.I’ve thought about trying a 300mA - there’s over 20 Rcbo’s
You say it's been ok for 2 weeks, then the nuisance tripping has started. You also mention the cabinet with the 100mA RCD is external. Is this tripping happening at the same time of day/night? Have the atmospheric conditions changed? I'm wondering if the cause may be condensation related.
You'd have to see if the disconnection times could be met based on Ze, have you I.R tested every circuit L-E and N-E ?

Suggestions:
Test the IR of electric ovens, hot wire element electric hobs, washing machines and tumble dryers and dishwashers, immersion heater.